[RE-wrenches] 3 phase off-grid UL listed
Eric Smiley
eric at vecoop.ca
Thu Sep 8 12:21:34 EDT 2022
I've worked with a few larger 3-phase Conext XW systems - 3 inverters and 6
inverters.
The inverters' output capabilities are slightly reduced since they have to
be converted to 120 V, effectively doubling the output current. Also,they
required an external transfer switch. Even with 3 inverters configured for
3-phase, I would recommend an external transfer. The relays have a habit of
welding.
Once they were configured properly, there was no problem starting large
HVAC loads and even large single phase loads were OK.
*Eric Smiley,* Project Manager
eric at vecoop.ca
T: 250.703.6004 <+12507036004>
T: 888.386.0116 <+18883860116>
*VIRIDIANENERGY.CA <https://viridianenergy.ca/>*
* <https://viridianenergy.ca/>*
On Thu, 8 Sept 2022 at 08:49, Vince McClellan via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> That’s a market segment that no inverter company that I know of really
> makes a product for.
> I would probably use 3 Sol-Ark 12K inverters.
> You’ll have to be careful with load balancing with any Sol-Ark inverter
> though.
> Schneider would also work but you will have a lot of individual components
> and you would need to be careful that the internal transfer switch is
> within its 60 amp capacity limit from a generator or other source. With
> multiple Schneider inverters there is the possibility that not all of the
> internal transfer switches will trip at exactly the same time causing the
> transfer switch in one inverter to take the whole load.
> I was originally a staunch Outback fan but we’ve stopped using their
> products after we had repeated Incidents of equipment not working right out
> of the box.
>
> Vince McClellan
> Energy Design
>
> On Sep 8, 2022, at 07:30, Jerry Shafer via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>
> Outback FX R can be built to be 3 phase and solark also works, for 30 k l
> would look at solark, 3 12's or 15's.
> Jerry
>
> On Thu, Sep 8, 2022, 4:42 AM Mac Lewis via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> Hello Wrenches,
>>
>> What inverter options are there for 3 phase, UL listed, off-grid inverter
>> systems in the 30kW+ category?
>> It's been quite a while since I dove into this...
>> Thanks!
>>
>> --
>>
>>
>>
>> Mac Lewis
>>
>> *"Yo solo sé que no sé nada." -Sócrates*
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220908/ef698840/attachment.htm>
More information about the RE-Wrenches
mailing list