[RE-wrenches] 3 phase off-grid UL listed

Vince McClellan vince at solarenergydesign.com
Thu Sep 8 11:49:40 EDT 2022


That’s a market segment that no inverter company that I know of really makes a product for. 
I would probably use 3 Sol-Ark 12K inverters. 
You’ll have to be careful with load balancing with any Sol-Ark inverter though. 
Schneider would also work but you will have a lot of individual components and you would need to be careful that the internal transfer switch is within its 60 amp capacity limit from a generator or other source. With multiple Schneider inverters there is the possibility that not all of the internal transfer switches will  trip at exactly the same time causing the transfer switch in one inverter to take the whole load. 
I was originally a staunch Outback fan but we’ve stopped using their products after we had repeated Incidents of equipment not working right out of the box.  

Vince McClellan 
Energy Design 

> On Sep 8, 2022, at 07:30, Jerry Shafer via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
> 
> 
> Outback FX R can be built to be 3 phase and solark also works, for 30 k l would look at solark, 3 12's or 15's.
> Jerry
> 
>> On Thu, Sep 8, 2022, 4:42 AM Mac Lewis via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>> Hello Wrenches,
>> 
>> What inverter options are there for 3 phase, UL listed, off-grid inverter systems in the 30kW+ category?  
>> It's been quite a while since I dove into this...
>> Thanks!
>> 
>> -- 
>> 
>> 
>> 
>> Mac Lewis
>> 
>> "Yo solo sé que no sé nada." -Sócrates
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: RE-wrenches at lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220908/df6f3ea7/attachment.htm>


More information about the RE-Wrenches mailing list