[RE-wrenches] Sol-Ark 15k
Michael Morningstar
mjmorningstar at gmail.com
Sun May 8 14:03:55 EDT 2022
We cut out the bottom plate entirely with a die grinder/cut off wheel and
then wrap the raw edge with vinyl "edge wrap" and set the inverters on top
of 10 x 10 x whatever gutters. The layout and sizes of Sol-Arks knock-outs
is screwy. Just need a bonding jumper between both enclosures. This is
common practice in the industrial world when dealing with large VFDs and
such.
On Sun, May 8, 2022 at 6:47 AM Jay via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Hi Chris,
>
> Can’t you increase the size of the KO’s?
>
> Jay
>
> On May 7, 2022, at 7:17 PM, Chris Sparadeo via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>
> Jason,
>
> I think I agree with your interpretation of the wiring diagram. My
> hesitation is, with a 1-1/4” KO for AC inputs, only choice seems to be a
> >24” stub conduit for 2/0 conductores to a fused disconnect. Not a fun pipe
> to bend…and extra BOS seems like a less than ideal solution.
>
> Is this your conclusion as well?
>
> On Sun, Apr 17, 2022 at 10:38 PM Darryl Thayer via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> Yes and no, I think this is a tap, "a tap shall be permitted anywhere
>> along a feeder" ' as long as it is less than a 10-foot rule or 25-foot
>> rule ending in a listed OCPD with a rating sufficient to handle the maximum
>> overcurrent'. Service equipment residential is rated for fault currents of
>> up to 10,000 amps withstand. Refer to 240.4.B and 240.21 (B) (1 & 2)
>>
>> On Sun, Apr 17, 2022 at 10:39 AM Jason Szumlanski via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>> But this isn't a tap. It's a feeder conductor connected to an OCPD.
>>>
>>> I guess if you don't have a grid in or generator in or AC Coupled PV,
>>> you could just call it an inverter output circuit and it could be sized
>>> accordingly. But it would still need to be protected at it's source by an
>>> appropriately rated OCPD. Don't get me wrong... I don't think there is a
>>> real safety issue here, but I also don't see how the NEC allows the
>>> conductor to be sized for anything less than 200A.
>>>
>>> Jason
>>>
>>>
>>> On Sun, Apr 17, 2022, 11:29 AM Darryl Thayer via RE-wrenches <
>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>>> The tap rule says you can reduce to 10% of the nominal size for 10 feet
>>>> and protect at the downstream OCPD or 25% for 25 feet for solar with
>>>> multiple sources see 705
>>>>
>>>> On Sat, Apr 16, 2022 at 9:16 PM Jason Szumlanski via RE-wrenches <
>>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>>
>>>>> That's what I'm thinking. You would need to use a 200A conductor to a
>>>>> separate load out OCPD before downsizing the wire. I guess there are pros
>>>>> and cons, but it seems this is geared toward whole house backup for 200A
>>>>> services. I'm eager to get an opportunity to use it in that scenario.
>>>>>
>>>>> Jason
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> On Sat, Apr 16, 2022, 10:06 PM Chris Sparadeo via RE-wrenches <
>>>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>>>
>>>>>> Jason,
>>>>>>
>>>>>> Any additional OCPD downstream of the 200A load output breaker could
>>>>>> allow for a smaller wire size to be used at these terminals. For example,
>>>>>> load output conductors run to a 100A main breaker panel board. Obviously
>>>>>> depending on circumstances, a #4 copper could fit the bill.
>>>>>>
>>>>>> What I’m not extremely excited about with the new design is that in
>>>>>> an off-grid scenario with a generator and smart load, we would now need to
>>>>>> integrate an AC disconnect for generator input (grid) and either a fused
>>>>>> disconnect or loads panel for any smart load output. With the 12K unit, the
>>>>>> integrated breakers help cut down on BOS and install time.
>>>>>>
>>>>>> -Chris
>>>>>>
>>>>>> On Sat, Apr 16, 2022 at 5:35 PM Darryl Thayer via RE-wrenches <
>>>>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>>>>
>>>>>>> Hello, The overcurrent device is to protect the conductors. you can
>>>>>>> put any size wire, but you must protect with the overcurrent device.
>>>>>>> REmember in solar equipment; you may have more than one supply source. The
>>>>>>> DC best example is solar modules connected in parallel, on
>>>>>>>
>>>>>>> On Fri, Apr 15, 2022 at 8:26 PM Jerry Shafer via RE-wrenches <
>>>>>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>>>>>
>>>>>>>> You must meet all expected source output potentials within the
>>>>>>>> design and operating limits, as long as the distribution panel and
>>>>>>>> connected wiring is rated for the max output of the protected source then
>>>>>>>> you are good. A 200 ATS connected to a 10 kW genny does not require 2/0 as
>>>>>>>> it will never meet that rating. Just remember its whatever the max output
>>>>>>>> can be plus your margin.
>>>>>>>>
>>>>>>>> On Fri, Apr 15, 2022, 5:44 PM Chris Sparadeo via RE-wrenches <
>>>>>>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>>>>>>
>>>>>>>>> Hi Jason,
>>>>>>>>>
>>>>>>>>> You bring up a valid point….in an off-grid scenario with the 15k
>>>>>>>>> do you size the conductors to the continuous capacity, surge capacity or
>>>>>>>>> the OCPD of the unit?
>>>>>>>>>
>>>>>>>>> -Chris
>>>>>>>>>
>>>>>>>>> On Fri, Apr 15, 2022 at 4:01 PM Jason Szumlanski via RE-wrenches <
>>>>>>>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>>>>>>>
>>>>>>>>>> P.S. ICYMI, this inverter has a massive combined AC coupled and
>>>>>>>>>> DC coupled capacity. They allow 15kWdc plus 19.2kWac!!! Impressive.
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>>
>>>>>>>>>> On Fri, Apr 15, 2022 at 10:59 AM Jason Szumlanski <
>>>>>>>>>> jason at floridasolardesigngroup.com> wrote:
>>>>>>>>>>
>>>>>>>>>>> I'm not following the wiring diagrams for this new inverter. It
>>>>>>>>>>> has 200A pass-through capability with an integrated 200A load disconnect.
>>>>>>>>>>> But then it says the wire gauge for the load out wiring can be #4 to 2/0.
>>>>>>>>>>>
>>>>>>>>>>> In an off-grid scenario where there is no generator, the max
>>>>>>>>>>> continuous output is 62.5A, so I assume 80A circuit protection could be
>>>>>>>>>>> used with 80A rated wire (#4), but how is that circuit protection
>>>>>>>>>>> implemented if the 200A breaker is integrated? Do you have to run a short
>>>>>>>>>>> piece of 2/0 to an external 80A rated OCPD and then step down to #4?
>>>>>>>>>>>
>>>>>>>>>>> Jason Szumlanski
>>>>>>>>>>>
>>>>>>>>>>>
>>>>>>>>>>>
>>>>>>>>>>>
>>>>>>>>>>>
>>>>>>>>>>> _______________________________________________
>>>>>>>>>>
>>>>>>>>>
>>>>>> _______________________________________________
>>>>>
>>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> --
> Chris Sparadeo
>
>
> C_802-369-4458
> H_802-728-3059
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
--
Michael Morningstar
Morningstar Electric
PO Box 1494
Mount Shasta, CA 96067
530-921-0560
mjmorningstar at gmail.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220508/8c593489/attachment.htm>
More information about the RE-Wrenches
mailing list