Hi Dave,
I typically use the same method you do for running conductors between two
non-continuous arrays. I have never had an issue with either AHJ blowback
or actual compromised conductors due to a lack of strain relief.
The only code reference I can think of is 300.4 regarding protection
against physical damage, but you have that covered with the use of a
secured conduit.
To appease the AHJ, you could add some pvc female adapters and gland seals.
Best,
Chris
On Tue, Mar 22, 2022 at 4:43 PM Dave Tedeyan <dave at sungineersolar.com>
wrote:
> Hi All,
>
> I have an inspector giving me a hard time about wire management between
> two ground mounted arrays. The racking is Unirac GFT, and the system was
> too large to have one continuous array. So there are two arrays, side by
> side, with only a 1' gap between the rails and modules from the two
> separate arrays.
>
> We jumped the PV wire between the arrays through a short section of PVC
> for protection, and the wires are secured to the rails about a foot past
> the PVC on either end. The inspector is citing the following:
> ----
> Array conductors found disconnected or improperly connected, which may be
> causing portions of the array to be inoperable and/or pose a shock hazard.
> ----
> They say that they are citing this because there is no strain relief as
> the wires enter and exit the 18" piece of conduit. My question to you all
> is, do you know of any code reference that says that this setup is or is
> not okay? I would also be curious to hear what others do to span a 1' gap
> on a ground mount. It almost seems as if I just left the conductors exposed
> for that gap, there would have been no problem.
>
> I attached a couple of photos to help with my written description.
> I appreciate the knowledge of this hive mind!
> Cheers,
> Dave
>
> --
> [image: Logo] <https://www.sungineersolar.com/>
> Dave Tedeyan, P.E.
> Owner | Sungineer Solar
> p: he | him | his
> a: 1653 Slaterville Rd.
> <https://www.google.com/maps/search/1653+Slaterville+Rd.+%C2%A0+%7C%C2%A0Ithaca,+NY+14850?entry=gmail&source=g>
>
> <https://www.google.com/maps/search/1653+Slaterville+Rd.+%C2%A0+%7C%C2%A0Ithaca,+NY+14850?entry=gmail&source=g>| Ithaca,
> NY 14850
> <https://www.google.com/maps/search/1653+Slaterville+Rd.+%C2%A0+%7C%C2%A0Ithaca,+NY+14850?entry=gmail&source=g>
> w: www.sungineersolar.com <http://www.sungineersolar.com/>
> c: (607) 288-2898
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> --
Chris Sparadeo
C_802-369-4458
H_802-728-3059
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220322/a4e7a9ac/attachment.htm>
More information about the RE-Wrenches
mailing list