In Florida, the AHJ is required to cite the section of code when rejecting
work. I always ask for that if rejected. I'm not sure how things work in NY.
You might start with 690.31(C)(1) that allows PV wire to be exposed within
the PV array. The array boundary is defined elsewhere as within 1 ft of the
array in all directions, although that pertains to rapid shutdown
specifically.
You're right - you might just remove the PVC and ask them how it doesn't
comply then, considering you only have to support it at 4.5 ft intervals.
Jason Szumlanski
Florida Solar Design Group
On Tue, Mar 22, 2022 at 4:43 PM Dave Tedeyan <dave at sungineersolar.com>
wrote:
> Hi All,
>
> I have an inspector giving me a hard time about wire management between
> two ground mounted arrays. The racking is Unirac GFT, and the system was
> too large to have one continuous array. So there are two arrays, side by
> side, with only a 1' gap between the rails and modules from the two
> separate arrays.
>
> We jumped the PV wire between the arrays through a short section of PVC
> for protection, and the wires are secured to the rails about a foot past
> the PVC on either end. The inspector is citing the following:
> ----
> Array conductors found disconnected or improperly connected, which may be
> causing portions of the array to be inoperable and/or pose a shock hazard.
> ----
> They say that they are citing this because there is no strain relief as
> the wires enter and exit the 18" piece of conduit. My question to you all
> is, do you know of any code reference that says that this setup is or is
> not okay? I would also be curious to hear what others do to span a 1' gap
> on a ground mount. It almost seems as if I just left the conductors exposed
> for that gap, there would have been no problem.
>
> I attached a couple of photos to help with my written description.
> I appreciate the knowledge of this hive mind!
> Cheers,
> Dave
>
> --
> [image: Logo] <https://www.sungineersolar.com/>
> Dave Tedeyan, P.E.
> Owner | Sungineer Solar
> p: he | him | his
> a: 1653 Slaterville Rd. | Ithaca, NY 14850
> w: www.sungineersolar.com <http://www.sungineersolar.com/>
> c: (607) 288-2898
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220322/7918c6b1/attachment.htm>
More information about the RE-Wrenches
mailing list