[RE-wrenches] alternatives to Outback GSLC xxxx box?

Tuss, Lones lones.tuss at enersys.com
Tue Mar 1 14:40:21 EST 2022


Hello Jason
yes the GSLC does come with a top. Please see Page 6 in the link below.
https://outbackpower.com/downloads/documents/inverter_chargers/radian_gs_load_center/gslc_plg_web.pdf
on the shunts as asked earlier in this thread
1000 amp 100mv
And
1500 amp 150 mv
Both have the same ration as the 500 amp 50mv normally supplied by OB
I hope this helps.


From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Rockisland
Sent: Tuesday, March 1, 2022 11:27 AM
To: William Miller <william at millersolar.com>; RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] alternatives to Outback GSLC xxxx box?


CAUTION: This email originated from outside of the Company. Do not click links or open attachments unless you recognize the sender and know the content is safe.

Hiya William,

Does the empty GSLC come with a top, or do you fabricate a top where the Radian usually bolts on? Would love to see a picture of your dead front hinge,  I always wanted to to that….
Thanks,

Jason Lerner
Waldron Power and Light Co.



On Mar 1, 2022, at 8:53 AM, William Miller <william at millersolar.com<mailto:william at millersolar.com>> wrote:

Kirk:

We purchase only the empty GSLC cabinets. They do include the breaker brackets and bus bars. I have received the cabinets missing hardware so check the inventory beforehand.

Here are a few hints you probably already know:

The shunts are the shoddiest construction and it is very easy to break the plastic base. Torque the upper shunt bolt after all other bus hardware is torqued.

I recommend using two 175A breakers. For some troubleshooting procedures it is necessary to isolate the two power modules.

An empty GSLC cabinet makes an acceptable PV recombiner. We cut off the bottom dead front tab and substitute a hinge. We wire the breakers with the dead font tilted out flat and all leads hinging at the bottom.

We never install any AC breakers in the GSLC cabinets. The back-wiring is just too awkward. Instead  we use outboard breaker panels or panel boards—one for Gen Fed and one for Inverter Fed.

For bypassing we fabricate custom slide plates bolted to the dead-front to interlock output breakers. It’s not listed but with good craftsmanship it looks official.

Here are a few photos:

https://millersolar.com/MillerSolar/Portfolio/Inverters/battery_iinverters/JP_Radian/JP_Radian.html<https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-d039a91ee15a4f6f&q=1&e=d5cbce0b-637f-4ba7-9869-6f109217c781&u=https%3A%2F%2Fmillersolar.com%2FMillerSolar%2FPortfolio%2FInverters%2Fbattery_iinverters%2FJP_Radian%2FJP_Radian.html>

I hope the above info is helpful.

William Miller

On Tue, Mar 1, 2022 at 6:23 AM Kirk Herander <kirkh at vermont.solar<mailto:kirkh at vermont.solar>> wrote:
All,

I am doing a multiple stacked Radian GS8048 system. And all I need in my design is two OB 175 a breakers in a box which integrates w/ each respective inverter. The manual bypass switch is useless, for all inverters need to be bypassed at once using a single external bypass. OB does not make a version of the GSLC which only has the inverter breakers. They do make an empty GSLC with nothing in it. But no mounting assembly for the breakers, and no add-on kit offering to do this either.
I thought Midnite made something compatible, but don't see it on their web site. Any ideas? Thanks.

--
Kirk Herander / kirkh at vermont.solar<mailto:kirkh at vermont.solar>
Owner|Principal, VT Solar, LLC
Celebrating our 31st Anniversary 1991-2022!!
www.vermont.solar<https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-e4ddc7164aca4f14&q=1&e=d5cbce0b-637f-4ba7-9869-6f109217c781&u=https%3A%2F%2Fnam02.safelinks.protection.outlook.com%2F%3Furl%3Dwww.vermontsolarnow.com%26data%3D02%257C01%257C%257C9f0330d75a244870112408d685311841%257C84df9e7fe9f640afb435aaaaaaaaaaaa%257C1%257C0%257C636842843233477645%26sdata%3D0NjyuKeQbEK6245SNnk8X4XnP9Q%252B%252BqtvcALkdDghvk4%253D%26reserved%3D0>
dba Vermont Solar Engineering
802.863.1202
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org<https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-7b396d10a42c0f44&q=1&e=d5cbce0b-637f-4ba7-9869-6f109217c781&u=http%3A%2F%2Fre-wrenches.org%2F>

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-a1bff427848a4564&q=1&e=d5cbce0b-637f-4ba7-9869-6f109217c781&u=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-b8ea30cbc06c75b2&q=1&e=d5cbce0b-637f-4ba7-9869-6f109217c781&u=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-c65f2c4f8389e144&q=1&e=d5cbce0b-637f-4ba7-9869-6f109217c781&u=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm>

Check out or update participant bios:
http://www.members.re-wrenches.org<https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-3373bc454b22cb3c&q=1&e=d5cbce0b-637f-4ba7-9869-6f109217c781&u=http%3A%2F%2Fwww.members.re-wrenches.org%2F>
--

William Miller
Miller Solar.com<https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-504602e41aee048f&q=1&e=d5cbce0b-637f-4ba7-9869-6f109217c781&u=http%3A%2F%2Fsolar.com%2F>
895-438-5600
www.millersolar.com<https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-18562c478088e59c&q=1&e=d5cbce0b-637f-4ba7-9869-6f109217c781&u=http%3A%2F%2Fwww.millersolar.com%2F>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org<https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-7b396d10a42c0f44&q=1&e=d5cbce0b-637f-4ba7-9869-6f109217c781&u=http%3A%2F%2Fre-wrenches.org%2F>

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-a1bff427848a4564&q=1&e=d5cbce0b-637f-4ba7-9869-6f109217c781&u=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-b8ea30cbc06c75b2&q=1&e=d5cbce0b-637f-4ba7-9869-6f109217c781&u=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-c65f2c4f8389e144&q=1&e=d5cbce0b-637f-4ba7-9869-6f109217c781&u=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm>

Check out or update participant bios:
http://www.members.re-wrenches.org<https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-3373bc454b22cb3c&q=1&e=d5cbce0b-637f-4ba7-9869-6f109217c781&u=http%3A%2F%2Fwww.members.re-wrenches.org%2F>



This email and any attachments may contain confidential information that is intended only for the recipient(s). If you have received this email in error, please notify the sender and delete it from your system. Any views or opinions presented in this email are solely those of the author and do not necessarily represent those of the company or its affiliates. This email does not constitute an agreement to conduct transactions by electronic means and does not create any legally binding contract or enforceable obligation in the absence of a fully signed written contract. The recipient should check this email and any attachments for viruses. The company accepts no liability for any loss or damage caused by software viruses. If you are the intended recipient and you do not wish to receive similar email(s) from us in the future then please notify the sender. Please consider the environment before printing.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220301/24b3d81c/attachment.htm>


More information about the RE-Wrenches mailing list