Thanks for the photos, they look good, gives me some ideas.

On Tue, Mar 1, 2022 at 12:31 PM William Miller <william at millersolar.com>
wrote:

> Kirk:
>
> We purchase only the empty GSLC cabinets. They do include the breaker
> brackets and bus bars. I have received the cabinets missing hardware so
> check the inventory beforehand.
>
> Here are a few hints you probably already know:
>
> The shunts are the shoddiest construction and it is very easy to break the
> plastic base. Torque the upper shunt bolt after all other bus hardware is
> torqued.
>
> I recommend using two 175A breakers. For some troubleshooting procedures
> it is necessary to isolate the two power modules.
>
> An empty GSLC cabinet makes an acceptable PV recombiner. We cut off the
> bottom dead front tab and substitute a hinge. We wire the breakers with the
> dead font tilted out flat and all leads hinging at the bottom.
>
> We never install any AC breakers in the GSLC cabinets. The back-wiring is
> just too awkward. Instead  we use outboard breaker panels or panel
> boards—one for Gen Fed and one for Inverter Fed.
>
> For bypassing we fabricate custom slide plates bolted to the dead-front to
> interlock output breakers. It’s not listed but with good craftsmanship it
> looks official.
>
> Here are a few photos:
>
>
> https://millersolar.com/MillerSolar/Portfolio/Inverters/battery_iinverters/JP_Radian/JP_Radian.html
>
> I hope the above info is helpful.
>
> William Miller
>
> On Tue, Mar 1, 2022 at 6:23 AM Kirk Herander <kirkh at vermont.solar> wrote:
>
>> All,
>>
>> I am doing a multiple stacked Radian GS8048 system. And all I need in my
>> design is two OB 175 a breakers in a box which integrates w/ each
>> respective inverter. The manual bypass switch is useless, for all inverters
>> need to be bypassed at once using a single external bypass. OB does not
>> make a version of the GSLC which only has the inverter breakers. They do
>> make an empty GSLC with nothing in it. But no mounting assembly for the
>> breakers, and no add-on kit offering to do this either.
>> I thought Midnite made something compatible, but don't see it on their
>> web site. Any ideas? Thanks.
>>
>> --
>>
>> *Kirk Herander / **kirkh at vermont.solar <kirkh at vermont.solar>*
>>
>> *Owner|Principal, VT Solar, LLC*
>>
>> *Celebrating our 31st Anniversary 1991-2022!!*
>>
>> *www.vermont.solar*
>> <https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0>
>>
>> dba Vermont Solar Engineering
>>
>> 802.863.1202
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> --
>
> William Miller
> Miller Solar.com
> 895-438-5600
> www.millersolar.com
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 

*Kirk Herander / **kirkh at vermont.solar <kirkh at vermont.solar>*

*Owner|Principal, VT Solar, LLC*

*Celebrating our 31st Anniversary 1991-2022!!*

*www.vermont.solar*
<https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0>

dba Vermont Solar Engineering

802.863.1202
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220301/97dcb908/attachment.htm>


More information about the RE-Wrenches mailing list