[RE-wrenches] alternatives to Outback GSLC xxxx box?
William Miller
william at millersolar.com
Tue Mar 1 11:53:22 EST 2022
Kirk:
We purchase only the empty GSLC cabinets. They do include the breaker
brackets and bus bars. I have received the cabinets missing hardware so
check the inventory beforehand.
Here are a few hints you probably already know:
The shunts are the shoddiest construction and it is very easy to break the
plastic base. Torque the upper shunt bolt after all other bus hardware is
torqued.
I recommend using two 175A breakers. For some troubleshooting procedures it
is necessary to isolate the two power modules.
An empty GSLC cabinet makes an acceptable PV recombiner. We cut off the
bottom dead front tab and substitute a hinge. We wire the breakers with the
dead font tilted out flat and all leads hinging at the bottom.
We never install any AC breakers in the GSLC cabinets. The back-wiring is
just too awkward. Instead we use outboard breaker panels or panel
boards—one for Gen Fed and one for Inverter Fed.
For bypassing we fabricate custom slide plates bolted to the dead-front to
interlock output breakers. It’s not listed but with good craftsmanship it
looks official.
Here are a few photos:
https://millersolar.com/MillerSolar/Portfolio/Inverters/battery_iinverters/JP_Radian/JP_Radian.html
I hope the above info is helpful.
William Miller
On Tue, Mar 1, 2022 at 6:23 AM Kirk Herander <kirkh at vermont.solar> wrote:
> All,
>
> I am doing a multiple stacked Radian GS8048 system. And all I need in my
> design is two OB 175 a breakers in a box which integrates w/ each
> respective inverter. The manual bypass switch is useless, for all inverters
> need to be bypassed at once using a single external bypass. OB does not
> make a version of the GSLC which only has the inverter breakers. They do
> make an empty GSLC with nothing in it. But no mounting assembly for the
> breakers, and no add-on kit offering to do this either.
> I thought Midnite made something compatible, but don't see it on their web
> site. Any ideas? Thanks.
>
> --
>
> *Kirk Herander / **kirkh at vermont.solar <kirkh at vermont.solar>*
>
> *Owner|Principal, VT Solar, LLC*
>
> *Celebrating our 31st Anniversary 1991-2022!!*
>
> *www.vermont.solar*
> <https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0>
>
> dba Vermont Solar Engineering
>
> 802.863.1202
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> --
William Miller
Miller Solar.com
895-438-5600
www.millersolar.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220301/48d6334b/attachment.htm>
More information about the RE-Wrenches
mailing list