[RE-wrenches] alternatives to Outback GSLC xxxx box?
Kirk Herander
kirkh at vermont.solar
Tue Mar 1 11:00:52 EST 2022
Thanks all. I just found it is included as mentioned in the GSLC
installation manual. Just not mentioned in the spec sheet about the
assembly.
On Tue, Mar 1, 2022 at 10:54 AM Kirpal <solarworks at gmail.com> wrote:
> Kirk. Good morning. The 175A breaker assembly is included in the bare
> GSLC box for the radians. You have to order the 175A breakers separately;
> they are not included. The bare box includes a 500A 50MV shunt, the
> breaker brackets to connect breakers to the inverter and that's it. No AC
> buss bars are included. Negative and ground buss bars are included.
> In a multi inverter system if 1000A 100mv shunt size is needed, note that
> you can not mix 500A and 1000A shunts on a single flexnet DC. It doesn't
> work. Shunts all have to be the same. I found this out the hard way.
>
> Sunny Regards,
> Kirpal Khalsa
> Oregon LRT#25
> Oregon Solarworks LLC
> www.oregonsolarworks.com
> 541-299-0402
>
>
> On Tue, Mar 1, 2022 at 6:23 AM Kirk Herander <kirkh at vermont.solar> wrote:
>
>> All,
>>
>> I am doing a multiple stacked Radian GS8048 system. And all I need in my
>> design is two OB 175 a breakers in a box which integrates w/ each
>> respective inverter. The manual bypass switch is useless, for all inverters
>> need to be bypassed at once using a single external bypass. OB does not
>> make a version of the GSLC which only has the inverter breakers. They do
>> make an empty GSLC with nothing in it. But no mounting assembly for the
>> breakers, and no add-on kit offering to do this either.
>> I thought Midnite made something compatible, but don't see it on their
>> web site. Any ideas? Thanks.
>>
>> --
>>
>> *Kirk Herander / **kirkh at vermont.solar <kirkh at vermont.solar>*
>>
>> *Owner|Principal, VT Solar, LLC*
>>
>> *Celebrating our 31st Anniversary 1991-2022!!*
>>
>> *www.vermont.solar*
>> <https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0>
>>
>> dba Vermont Solar Engineering
>>
>> 802.863.1202
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
--
*Kirk Herander / **kirkh at vermont.solar <kirkh at vermont.solar>*
*Owner|Principal, VT Solar, LLC*
*Celebrating our 31st Anniversary 1991-2022!!*
*www.vermont.solar*
<https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0>
dba Vermont Solar Engineering
802.863.1202
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220301/959c8f61/attachment.htm>
More information about the RE-Wrenches
mailing list