Thanks for offering Darryl, but I have pretty good data on the 120/240VAC
single phase motor I am up against. NEC 430 suggests LRC is 188 A, but I am
measuring more like 112A during start up. I am thinking that using the VFD
for slower ramp up AND as a phase converter from single phase to three
phase will help lower inrush significantly.

Jay-  with the autotransformer option, I was hoping that the 240V input and
240V output capability of the Victron autotransformer would add some of the
benefits of a transformer based inverter to the Sol Ark's transformer-less
design. Less about balancing phases and more about adding some inductive
kick when the load drops. Am I correct in thinking this is a possible use
of this specific device?

On Mon, Jan 31, 2022 at 9:43 AM Darryl Thayer <darylsolar1 at gmail.com> wrote:

> Hi i have a single phase motor at a old install that i replaced about
> 8 years ago.  Would it help if i made some starting load surge measurments?
>
> On Fri, Jan 28, 2022, 11:52 PM Darryl Thayer <darylsolar1 at gmail.com>
> wrote:
>
>> Hi Chris, In the past, I was able to start a 5 hp pump motor using a VFD.
>> , I can not remember the make, of the VFD but I think it was an ABB 7.5 or
>> 10 HP connected to a single-phase motor.  I started it on two Outback 3548s
>> (or maybe 3024s).  Now for the tricky part, I have done this several times
>> over the years so I keep confusing the systems.  you must power the VFD
>> before starting the motor to charge the capacitors as the VFD will also
>> have a loading surge.( one time on maybe 10 HP I did a homemade resistor)
>> The VFD has a large capacitance and will have a surge.  Most water pumps do
>> not have a high zero-speed torque requirement, meaning low inertia, so you
>> can use a slower ramp to speed.  watch your speed as the VFD can Overspeed
>> the motor increasing the load.  The advantage of the VFD is it can run at a
>> lower speed reducing the load on the inverter.  I also think an Auto
>> Transformer will balance the load between the inverters, but may not be
>> necessary.
>> Also be aware that starting surge is on the battery also,  If your motor
>> has aGH motor it can have a 4 to7 times the running loads on starting.  NEC
>> 430,7 I think.  This can be well over 100 amps.  The inverter will sag in
>> voltage during startup but they may draw 400 or 500 amps from the battery.
>> If my memory is correct the 10 HP VFD has the possibility of adding an
>> extra capacitor which reduces AC starting draw.
>> Sorry, this was so long, it was more than 20 years ago for me.
>>
>>
>> On Fri, Jan 28, 2022 at 10:46 AM Chris Sparadeo <sparadeo.chris at gmail.com>
>> wrote:
>>
>>> Hi all,
>>>
>>> I currently have an off-grid client that has a 120/240VAC  7.5 HP -  40A
>>> FLC single phase pool pump. Locked rotor current is around 110 A. I had
>>> initially (and naively) thought that two Sol Ark 12k units would be able to
>>> handle this load. Due to the lack of a transformer, the unit's just can't
>>> output the required inductive startup inrush. Now getting clarification
>>> from Sol Ark that max inductive HP output is 2.5 HP per unit. We had
>>> installed an amply sized SR35 soft starter, with no avail. The 20 kW
>>> generator can start the motor, but it is noticeably shaken with the
>>> intense load drop.
>>>
>>> I am toying with the idea of installing a VFD and upgrading the pool
>>> pump to a three phase motor. Would make for a much smoother ramp and self
>>> start. The client is a bit hesitant to upgrade and would like to continue
>>> using their clunky, non-self starting single phase motor.
>>>
>>> My other thought was to implement an autotransformer to add some copper
>>> to the equation and help the Sol Ark's get the job done. Has anyone had any
>>> experience with the Victron 100A autotransformer for both 120/240 input and
>>> output?
>>>
>>> Any suggestions or relative experience would be greatly appreciated!
>>>
>>> -Kindly,
>>>
>>> -Chris
>>>
>>> --
>>>
>>> *Chris Sparadeo *
>>>
>>> *NABCEP Certified PV Installation Professional **® **# 042919-015652*
>>>
>>> *NABCEP Certified PV System Inspector **®** # 052920-015652 *
>>>
>>> *State of Vermont Journeyman Electrician # EJ-07619*
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220131/9ccc4691/attachment.htm>


More information about the RE-Wrenches mailing list