[RE-wrenches] Autotransformer for Single Phase Motor Headache
Darryl Thayer
darylsolar1 at gmail.com
Mon Jan 31 09:42:51 EST 2022
Hi i have a single phase motor at a old install that i replaced about
8 years ago. Would it help if i made some starting load surge measurments?
On Fri, Jan 28, 2022, 11:52 PM Darryl Thayer <darylsolar1 at gmail.com> wrote:
> Hi Chris, In the past, I was able to start a 5 hp pump motor using a VFD.
> , I can not remember the make, of the VFD but I think it was an ABB 7.5 or
> 10 HP connected to a single-phase motor. I started it on two Outback 3548s
> (or maybe 3024s). Now for the tricky part, I have done this several times
> over the years so I keep confusing the systems. you must power the VFD
> before starting the motor to charge the capacitors as the VFD will also
> have a loading surge.( one time on maybe 10 HP I did a homemade resistor)
> The VFD has a large capacitance and will have a surge. Most water pumps do
> not have a high zero-speed torque requirement, meaning low inertia, so you
> can use a slower ramp to speed. watch your speed as the VFD can Overspeed
> the motor increasing the load. The advantage of the VFD is it can run at a
> lower speed reducing the load on the inverter. I also think an Auto
> Transformer will balance the load between the inverters, but may not be
> necessary.
> Also be aware that starting surge is on the battery also, If your motor
> has aGH motor it can have a 4 to7 times the running loads on starting. NEC
> 430,7 I think. This can be well over 100 amps. The inverter will sag in
> voltage during startup but they may draw 400 or 500 amps from the battery.
> If my memory is correct the 10 HP VFD has the possibility of adding an
> extra capacitor which reduces AC starting draw.
> Sorry, this was so long, it was more than 20 years ago for me.
>
>
> On Fri, Jan 28, 2022 at 10:46 AM Chris Sparadeo <sparadeo.chris at gmail.com>
> wrote:
>
>> Hi all,
>>
>> I currently have an off-grid client that has a 120/240VAC 7.5 HP - 40A
>> FLC single phase pool pump. Locked rotor current is around 110 A. I had
>> initially (and naively) thought that two Sol Ark 12k units would be able to
>> handle this load. Due to the lack of a transformer, the unit's just can't
>> output the required inductive startup inrush. Now getting clarification
>> from Sol Ark that max inductive HP output is 2.5 HP per unit. We had
>> installed an amply sized SR35 soft starter, with no avail. The 20 kW
>> generator can start the motor, but it is noticeably shaken with the
>> intense load drop.
>>
>> I am toying with the idea of installing a VFD and upgrading the pool pump
>> to a three phase motor. Would make for a much smoother ramp and self start.
>> The client is a bit hesitant to upgrade and would like to continue using
>> their clunky, non-self starting single phase motor.
>>
>> My other thought was to implement an autotransformer to add some copper
>> to the equation and help the Sol Ark's get the job done. Has anyone had any
>> experience with the Victron 100A autotransformer for both 120/240 input and
>> output?
>>
>> Any suggestions or relative experience would be greatly appreciated!
>>
>> -Kindly,
>>
>> -Chris
>>
>> --
>>
>> *Chris Sparadeo *
>>
>> *NABCEP Certified PV Installation Professional **® **# 042919-015652*
>>
>> *NABCEP Certified PV System Inspector **®** # 052920-015652 *
>>
>> *State of Vermont Journeyman Electrician # EJ-07619*
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220131/b9501938/attachment.htm>
More information about the RE-Wrenches
mailing list