[RE-wrenches] High Voltage Breakers for Conext Mppt-80-600
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Wed Jan 26 18:03:14 EST 2022
Eric, definitely what I had seen when we offgrid field tested the mppt-
80 in 2010 ! Totally bullet proof charger and the SQD disco shows there are
127 on the west coast for $115 HU361RB. Typically this is outside and
protected where it belongs. It is fine next to the mppt if needed. Just do
not land 600vdc in the PDP if you want code compliance and safety of the
power system.
The newer Mppt-100-600 is just as robust.
Dave Angelini
Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail offgridsolar at sti.net
[2]
text 209 813 0060
On Wed, 26 Jan 2022 13:10:12 -0800, Eric Smiley
wrote: I looked up the CSA record for the XW PDP and it shows:
*
Maximum System Voltage (DC) 150V dc
* Maximum Battery System Voltage 62 V
dc (48V nominal)
* Maximum System Voltage (AC) 140/280V ac
ERIC SMILEY,
Project Manager
eric at vecoop.ca [3]
T: 250.703.6004 [4]
T: 888.386.0116
[5]
On Wed, 26 Jan 2022 at 12:53, William Miller wrote:
Dave:
With all due respect, I don't see this as an issue. All of our building
wire is rated at 600 volts. If you segregate your OPCD, work neatly and
bundle your various lead groupings I think it is perfectly safe. If one is
real paranoid, you could rivet in some partitions or more simply, sleeve
the 600 VDC leads in NMLT.
I looked all through the documentation for the
cabinets and no voltage rating is given. We cannot assume the rating is a
limitation until we find one. Let us all know if you are privy to this
detail.
I would not hesitate to integrate the 600 volt rated Conext
branded charge controllers into Conext branded BOS cabinets as long as the
workmanship is good.
William Miller
Miller Solar
17395 Oak Road,
Atascadero, CA 93422
805-438-5600
www.millersolar.com [7]
CA Lic.
773985
FROM: Dave Angelini Offgrid Solar [mailto:offgridsolar at sti.net
[8]]
SENT: Wednesday, January 26, 2022 11:15 AM
TO:
william at millersolar.com [9]; RE-wrenches
SUBJECT: Re: [RE-wrenches] High
Voltage Breakers for Conext Mppt-80-600
It is 600vdc ! Do you want that
in a PDP with your 48Vdc and 120/240vac? I do not believe it to be UL
listed for 600vdc in there, and so you are breaking some pretty big rules
here. I do not post much anymore here. Keep 600vdc out of the PDP and for
Offgrid we always want high reliability. Just good design practice!
DAVE
ANGELINI OFFGRID SOLAR
"WE GO WHERE POWERLINES DON'T"
E-MAIL
TEXT 209
813 0060
Links:
------
[1]
http://members.sti.net/offgridsolar/
[2] mailto:offgridsolar at sti.net
[3]
mailto:eric at vecoop.ca
[4] http://webmail.sti.net/tel:+12507036004
[5]
http://webmail.sti.net/tel:+18883860116
[6]
mailto:william at millersolar.com
[7] http://www.millersolar.com/
[8]
mailto:offgridsolar at sti.net
[9] mailto:william at millersolar.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220126/cc5330d4/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: blocked.gif
Type: image/gif
Size: 118 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220126/cc5330d4/attachment.gif>
More information about the RE-Wrenches
mailing list