[RE-wrenches] Sol-Ark AC Coupling Issues
Vince McClellan
vince at solarenergydesign.com
Thu Jan 20 13:32:23 EST 2022
Thanks again for your input. I'll check the Blue Ion battery voltage the
next time on site with and without the Radian AC coupled. I'm also going to
check in with Sol-Ark and see if the inverters respond to high battery
voltage when they are in closed loop with the BMS on the battery. I've
always assumed that the Sol-Ark's software just responds to the SOC from
the BMS.
That would be a possible connection between the freq-watt function on the
Sol-Ark and DC power from the solar array. I was really scratching my head
on where the possible connection could be between incoming DC power and the
freq-watt function on the Sol-Arks.
Vince McClellan
Energy Design
NABCEP PV Installation Professional
p. (541) 485-8122 f. (541) 338-8202
If you have received this email and are not the intended recipient please
delete this email. Copying, or using any part, content, or attachment of
this email is strictly prohibited.
On Thu, Jan 20, 2022 at 6:41 AM Pieter Huebner <
pieter at offgridenterprises.org> wrote:
> Vince, Although you have an AC bussed connection, the issue may not be the
> opposite as ours. In Our case the battery buss voltage goes high when the
> solar array is enabled. If you are also experiencing DC buss excursions you
> can trigger frequency shifting. If you haven't already done so, I suggest
> that you closely monitor the battery voltage when the solar array is
> charging both with and without the Radian AC bussing connected.
>
> Pieter
>
>
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Vince McClellan
> *Sent:* Wednesday, January 19, 2022 11:16 PM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Subject:* Re: [RE-wrenches] Sol-Ark AC Coupling Issues
>
>
>
> Thanks Pieter
>
> We seem to have the opposite problem from what you are experiencing. Our
> freq-watt regulation of the Radian inverter by the Sol-Ark inverters seems
> to be actuated by the DC power from the solar array that is DC connected to
> the Sol-Ark inverters. It is supposed to be actuated by the SOC of the Blue
> Ion batteries, but that is inconsistent at best. We can turn the DC power
> from the solar array on on the master inverter, but when we try using the
> MPPT channels on the two other inverters it briefly actuates the freq-watt
> function of the Sol-Ark disconnecting the Radian inverter.
>
>
> Vince McClellan
>
> Energy Design
>
> NABCEP PV Installation Professional
>
> p. (541) 485-8122 f. (541) 338-8202
>
> If you have received this email and are not the intended recipient please
> delete this email. Copying, or using any part, content, or attachment of
> this email is strictly prohibited.
>
>
>
>
>
> On Wed, Jan 19, 2022 at 8:20 PM Pieter Huebner <
> pieter at offgridenterprises.org> wrote:
>
> Vince, For what it is worth:
>
> We have also been working on similar issues when using multiple Solark
> inverters connected in parallel. The issue has been that parallel Solark
> inverters don't seem to be able to properly regulate the battery charge
> voltage. Although Solark technical support has been outstanding, and with
> their help we have diminished the severity but not solved the issue. For
> the sites that we currently have deployed for the interim we had to resort
> to turning down the charge voltage set points in order to protect the
> Lithium batteries. and avoid BMS shutdowns. We have a client with an
> existing outback system and were planning to expand the existing system
> using AC bussed Solark 12K inverters with additional battery and solar
> capacity (the site is 100% off grid, and has evolved into a micro grid),
> but are now going a different direction. Although we have not yet attempted
> an AC bussed Solark system, I suspect that the issues you are having are
> related to the battery voltage regulation problem we have experienced.
>
> Pieter
>
>
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Vince McClellan
> *Sent:* Wednesday, January 19, 2022 5:16 PM
> *To:* RE-wrenches <RE-wrenches at lists.re-wrenches.org>
> *Subject:* [RE-wrenches] Sol-Ark AC Coupling Issues
>
>
>
> Is anyone on the list familiar with AC coupling Sol-Ark inverters?
>
>
>
> We haven't been able to AC couple an existing Outback Radian system to a
> new system that we built with 3, Sol-Ark 12K inverters and 3, Blue Ion
> batteries. Each time we have tested the system the Sol-Ark inverters accept
> the power from the Radian inverter until we turn on the DC power from the
> new solar array to the Sol-Ark inverters. As soon as there is
> significant DC power coming from the solar array the Sol-Ark inverters
> freq-watt turns on for a brief second and disconnects the Radian inverter
> even when the Blue Ion batteries are below the programmed state of charge
> threshold. If we don't turn on the DC power from the new solar array the
> Radian will connect and stay connected.
>
>
>
> We have been working with Sol-Ark for several months now to get this
> system to accept the incoming power from the Radian without freq-watt
> kicking in on the Sol-Ark inverters and disconnecting the Radian inverter.
> Sol-Ark has sent two software revisions to the Sol-Ark inverters and we are
> still experiencing the same problem.
>
>
>
> Can anyone think of what we might be missing and where to direct our
> troubleshooting efforts next?
>
>
>
> Thanks,
>
>
> Vince McClellan
>
> Energy Design
>
> NABCEP PV Installation Professional
>
> p. (541) 485-8122 f. (541) 338-8202
>
> If you have received this email and are not the intended recipient please
> delete this email. Copying, or using any part, content, or attachment of
> this email is strictly prohibited.
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220120/d1e70cf9/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 181790 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220120/d1e70cf9/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 181790 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220120/d1e70cf9/attachment-0001.png>
More information about the RE-Wrenches
mailing list