[RE-wrenches] PAE series surge capacity/ power factor ?

larrycrutcher larry at starlightsolar.com
Sun Jan 9 15:15:26 EST 2022


Hi Jeremy,

Do you recall my email from May 28, 2021? I explained our experience and solution. I have attached it below for reference.

Larry Crutcher
Starlight Solar Power Systems


On May 28, 2021, at 9:03 AM, larry at starlightsolar.com wrote:
Hello Jeremy,

For more than a decade we have been aware of this issue wit Magnum Energy inverters. This primarily happened with the washer brand Splendide but other motors run by electronic controllers have caused the issue as well.  

When the washer is powered by Magnum inverters, the AC waveform becomes very distorted. You can view this on a scope as in the attached image. When you try to power other complex loads at the same time, the inverter can’t sufficiently emulate a sine wave.

We found a simple solution. Install a high frequency inverter for the washer only. A 600W GoPower (made by Cotek) inverter has worked for us. They are cheap but well made with great support.

Larry Crutcher
Starlight Solar Power Systems

Magnum inverter running Splendide washer, Voltage(top) and current.





On Jan 9, 2022, at 12:36 PM, Jeremy Rodriguez <allsolarjeremy at msn.com> wrote:


> 
> Hello
> we have a lot of PAE series magnum inverters out there.
> One client lately has been experiencing voltage drop and failure of PCBs in two of his household appliances.  I know it’s common to have some dimming of the lights when a well pump or other large load kicks on, but has anyone ran across a solution to alleviate the problem or boost up the voltage / condition it, in any way ?
> I’m not sure if this just happens with low battery voltage, or always 
> The inverter is located ~ 300 ft from the main electrical panel with #2/2/2/4 URD feeders to an outdoor disco, then 8 AWG copper to the mains panel. 
> 4448 PAE with one string of 6CS21P Batteries. 
> 
> 
Jeremy Rodriguez 
Solar Installation / Design Expert 
All Solar, Inc.
1453 M St
Penrose Colorado 



-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220109/8070c696/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Magnum Splendide washer 50MF cap.png
Type: image/png
Size: 620539 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220109/8070c696/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: splendide before.JPG
Type: image/jpeg
Size: 19669 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220109/8070c696/attachment.jpe>


More information about the RE-Wrenches mailing list