That was a quick solve, thanks Wrench Dan at Foxfire + Lones at Outback who
called me after 5PM on a Friday evening. For future search indexing
reference on this list (which I do a LOT):
Inverter 12VDC output controlling AGS MUST be on Port 1 on the Outback Hub.
Problem solved.

Dan Fink
Buckville Energy Consulting
970-672-4342

On Fri, Jan 7, 2022, 15:11 Foxfire Energy <dan at foxfire-energy.com> wrote:

> Seems I was once advised to drive the AGS goodies from the Master (P1).
>
> Sent from my iPhone
>
> > On Jan 7, 2022, at 5:02 PM, Dan Fink <danbob88 at gmail.com> wrote:
> >
> > 
> > Wrenches; Having a frustrating problem here with a Mate 3s and 2-wire
> AGS. The generator starts and stops fine from the Mate 3 AND via Optics RE
> from my smartphone,  but will not autostart by either SOC or Voltage. It is
> wired to use the inverter (VFXR 3524A) 12vdc aux output to an Outback relay
> board in the gen  as I've had issues in the past using the FNDC relay (as I
> think other Wrenches have too). The Mate 3s AGS is set for the Inverter
> port (4).
> >
> > In the past on other Mate 3s systems, I seem to remember always making
> sure the Inverter AUX relay mode is set to REMOTE to allow the Mate 3s to
> control the gen instead of the very limited GEN FAULT AGS setting in the
> inverter. But when I pull that up both via Optics and the Mate 3s itself,
> there IS no "remote" option anymore. The Mate3s firmware was updated last
> month to the latest version.
> >
> > If the REMOTE setting for the VFXR inverter no longer exists, what do I
> set the inverter AUX relay for to enable the Mate 3s advanced AGS to assume
> control? Or should I delegate AGS responsibilities to one of the FX PV
> controllers , just re-routing the 2 genstart wires? Not to the FNDC I
> assume because of those past problems.
> >
> > I'm pretty sure this issue has to be conflicting AGS instructions from
> different components, as sitting here at the kitchen table at the client's
> off grid house I can start and stop the gen from my phone!
> >
> > Thanks for any suggestions!
> >
> > Dan Fink
> > Buckville Energy Consulting LLC
> > 970-672-4342
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20220107/6268e3bf/attachment.htm>


More information about the RE-Wrenches mailing list