[RE-wrenches] Outback Mate 3s AGS problems

Tuss, Lones lones.tuss at enersys.com
Fri Jan 7 19:37:45 EST 2022


Hi Dan
Looks like we got it figured out with a phone call.
It is nice to have the system up on optics so we could look together.
If anyone was curious about the issue here. The Master inverter has to be in port 1.
Once that was done it came together pretty easily.
Put the inverter in Port 1 set AGS to port 1.
Perform a  2 minute voltage start.
Then Go Home its Friday Night
Take Care All



-----Original Message-----
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Foxfire Energy
Sent: Friday, January 7, 2022 2:11 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Outback Mate 3s AGS problems

CAUTION: This email originated from outside of the Company. Do not click links or open attachments unless you recognize the sender and know the content is safe.


Seems I was once advised to drive the AGS goodies from the Master (P1).

Sent from my iPhone

> On Jan 7, 2022, at 5:02 PM, Dan Fink <danbob88 at gmail.com> wrote:
>
> 
> Wrenches; Having a frustrating problem here with a Mate 3s and 2-wire AGS. The generator starts and stops fine from the Mate 3 AND via Optics RE from my smartphone,  but will not autostart by either SOC or Voltage. It is wired to use the inverter (VFXR 3524A) 12vdc aux output to an Outback relay board in the gen  as I've had issues in the past using the FNDC relay (as I think other Wrenches have too). The Mate 3s AGS is set for the Inverter port (4).
>
> In the past on other Mate 3s systems, I seem to remember always making sure the Inverter AUX relay mode is set to REMOTE to allow the Mate 3s to control the gen instead of the very limited GEN FAULT AGS setting in the inverter. But when I pull that up both via Optics and the Mate 3s itself, there IS no "remote" option anymore. The Mate3s firmware was updated last month to the latest version.
>
> If the REMOTE setting for the VFXR inverter no longer exists, what do I set the inverter AUX relay for to enable the Mate 3s advanced AGS to assume control? Or should I delegate AGS responsibilities to one of the FX PV controllers , just re-routing the 2 genstart wires? Not to the FNDC I assume because of those past problems.
>
> I'm pretty sure this issue has to be conflicting AGS instructions from different components, as sitting here at the kitchen table at the client's off grid house I can start and stop the gen from my phone!
>
> Thanks for any suggestions!
>
> Dan Fink
> Buckville Energy Consulting LLC
> 970-672-4342
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-7b396d10a42c0f44&q=1&e=6e31d3f5-c9bb-4494-b575-259ca78441ed&u=http%3A%2F%2Fre-wrenches.org%2F
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-a1bff427848a4564&q=1&e=6e31d3f5-c9bb-4494-b575-259ca78441ed&u=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-b8ea30cbc06c75b2&q=1&e=6e31d3f5-c9bb-4494-b575-259ca78441ed&u=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org
>
> List rules & etiquette:
> https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-c65f2c4f8389e144&q=1&e=6e31d3f5-c9bb-4494-b575-259ca78441ed&u=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm
>
> Check out or update participant bios:
> https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-3373bc454b22cb3c&q=1&e=6e31d3f5-c9bb-4494-b575-259ca78441ed&u=http%3A%2F%2Fwww.members.re-wrenches.org%2F
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-7b396d10a42c0f44&q=1&e=6e31d3f5-c9bb-4494-b575-259ca78441ed&u=http%3A%2F%2Fre-wrenches.org%2F

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-a1bff427848a4564&q=1&e=6e31d3f5-c9bb-4494-b575-259ca78441ed&u=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-b8ea30cbc06c75b2&q=1&e=6e31d3f5-c9bb-4494-b575-259ca78441ed&u=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org

List rules & etiquette:
https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-c65f2c4f8389e144&q=1&e=6e31d3f5-c9bb-4494-b575-259ca78441ed&u=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm

Check out or update participant bios:
https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-3373bc454b22cb3c&q=1&e=6e31d3f5-c9bb-4494-b575-259ca78441ed&u=http%3A%2F%2Fwww.members.re-wrenches.org%2F



This email and any attachments may contain confidential information that is intended only for the recipient(s). If you have received this email in error, please notify the sender and delete it from your system. Any views or opinions presented in this email are solely those of the author and do not necessarily represent those of the company or its affiliates. This email does not constitute an agreement to conduct transactions by electronic means and does not create any legally binding contract or enforceable obligation in the absence of a fully signed written contract. The recipient should check this email and any attachments for viruses. The company accepts no liability for any loss or damage caused by software viruses. If you are the intended recipient and you do not wish to receive similar email(s) from us in the future then please notify the sender. Please consider the environment before printing.


More information about the RE-Wrenches mailing list