[RE-wrenches] Rapid Shutdown Control for a System for a Multimode System Adding an Array to a Subpanel in Garage

Jay jay.peltz at gmail.com
Tue Nov 23 13:05:26 EST 2021


Hi Christopher 

If it is a newer radian then it has an ac coupling mode. 

When the batteries start to reach the charge set point, the inverter starts pushing the hz up snd up. Once it gets to 64, all new GT inverters shut off, including enphase. 

Voltage drops, hz drops, 5 minute delay, rinse and repeat. It’s a a great feature for infrequent control needs. 

This only comes into play when the grid is down and the batteries are full. 

I hope this helps. 

Jay
Peltz power. 

> On Nov 23, 2021, at 9:42 AM, Christopher Warfel <cwarfel at entech-engineering.com> wrote:
> 
> 
> It was tough for me to figure out how to write my email and not make it confusing.  
> 
> What I am worried about is the microinverter system operating when the utility goes down and the microinverters continuing to operate and charge the batteries as a load.  I need to disconnect the microinverter circuit only when the batteries are fully charged in grid isolated mode.  All the ways I can think of that would normally work to deenergize the microinverters automatically based upon battery voltage won't work.  I can submit a drawing if that would help. I am trying not to run another conductor circuit from the house to the garage.  I realize that would solve the problem, but it is an expensive solution.  English is my foreign native language. 
> 
> 
> 
> On 11/23/2021 10:39 AM, August Goers wrote:
>> Hi Chris - If I'm following you right, you have a PV system on a detached garage that ties into a backup subpanel also in the garage? The code only requires the RSID (rapid shutdown initiation device) to be on the exterior of the building. Would it work to put the RSID on the garage exterior? You could route your PV circuits to a switch or switches on the exterior of the garage on the way down to the sub it ties into. You could also use a shunt trip breaker(s) for the PV circuit(s). If for some reason you need to have the RSID on the main house, it gets trickier. Might need to trench?
>> 
>> August
>> Luminalt
>> 
>> 
>> On Tue, Nov 23, 2021 at 7:24 AM Christopher Warfel <cwarfel at entech-engineering.com> wrote:
>>> I would appreciate ideas on how to shut down a proposed microinverter system on a garage that is 100% serviced by an Outback Radian multimode system in the main building that has the garage on the back up service panel in the main building.
>>> 
>>> Garage has a MLO subpanel that is connected to the multimode back up service panel that is in the main building.
>>> 
>>> If grid goes down, we need to disconnect the microinverter array so it does not overcharge the battery system. If we use the battery voltage relay, we will take out all the garage circuits, which would disable its heating system, etc. We just want to disconnect the microinverter circuit in the garage subpanel.
>>> 
>>> Does anyone know of a product that could do this. I would imagine a transmitter, or perhaps something else besides a microinverter array? 
>>> 
>>> 
>>> 
>>> Thanks for any help. Chris
>>> 
>>> 
>>> 
>>> 
>>> 
>>> 
>>> 
>>> -- 
>>>                                          Christopher Warfel
>>>                      ENTECH Engineering, Inc.
>>> PO Box 871, Block Island, RI 02807
>>>                                                             401-466-8978
>>> <EEIlogolong.jpg>
>>> 
>>> 
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> Pay optional member dues here: http://re-wrenches.org
>>> 
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> There are two list archives for searching. When one doesn't work, try the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>> 
> -- 
>                                          Christopher Warfel
>                      ENTECH Engineering, Inc.
> PO Box 871, Block Island, RI 02807
>                                                             401-466-8978
> <EEIlogolong.jpg>
> 
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20211123/75bd3240/attachment.htm>


More information about the RE-Wrenches mailing list