It was tough for me to figure out how to write my email and not make it
confusing.
What I am worried about is the microinverter system operating when the
utility goes down and the microinverters continuing to operate and
charge the batteries as a load. I need to disconnect the microinverter
circuit only when the batteries are fully charged in grid isolated
mode. All the ways I can think of that would normally work to
deenergize the microinverters automatically based upon battery voltage
won't work. I can submit a drawing if that would help. I am trying not
to run another conductor circuit from the house to the garage. I
realize that would solve the problem, but it is an expensive solution.
English is my foreign native language.
On 11/23/2021 10:39 AM, August Goers wrote:
> Hi Chris - If I'm following you right, you have a PV system on a
> detached garage that ties into a backup subpanel also in the garage?
> The code only requires the RSID (rapid shutdown initiation device) to
> be on the exterior of the building. Would it work to put the RSID on
> the garage exterior? You could route your PV circuits to a switch or
> switches on the exterior of the garage on the way down to the sub it
> ties into. You could also use a shunt trip breaker(s) for the PV
> circuit(s). If for some reason you need to have the RSID on the main
> house, it gets trickier. Might need to trench?
>
> August
> Luminalt
>
>
> On Tue, Nov 23, 2021 at 7:24 AM Christopher Warfel
> <cwarfel at entech-engineering.com> wrote:
>
> I would appreciate ideas on how to shut down a proposed
> microinverter system on a garage that is 100% serviced by an
> Outback Radian multimode system in the main building that has the
> garage on the back up service panel in the main building.
>
> Garage has a MLO subpanel that is connected to the multimode back
> up service panel that is in the main building.
>
> If grid goes down, we need to disconnect the microinverter array
> so it does not overcharge the battery system. If we use the
> battery voltage relay, we will take out all the garage circuits,
> which would disable its heating system, etc. We just want to
> disconnect the microinverter circuit in the garage subpanel.
>
> Does anyone know of a product that could do this. I would imagine
> a transmitter, or perhaps something else besides a microinverter
> array?
>
>
> Thanks for any help. Chris
>
>
>
>
> --
> Christopher Warfel
> ENTECH Engineering, Inc.
> PO Box 871, Block Island, RI 02807
> 401-466-8978
> <http://entech-engineering.com>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work,
> try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
--
Christopher Warfel
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978
<http://entech-engineering.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20211123/4ffe8eb2/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EEIlogolong.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20211123/4ffe8eb2/attachment.jpg>
More information about the RE-Wrenches
mailing list