Years ago we tried using the relay in the FNDC with a system of sealed
Outback FX inverters. After a few times call backs about the generator
being left running long after it should have stopped, I discovered that
the problem was indeed caused by the relay in the FNDC. That relay is a
latching type and Outback sends the signal for it to change state only
once; they don't check to see if it actually changed state (apparently
the hardware wasn't set up to allow that); and they don't send a second
signal to improve the chance of a successful operation. You know the
screen in the Mate where they keep a tally of communication errors, not
sure that is comm errors at unfortunate times are the cause or not, but
I suspect it is. Maybe the relay in this FNDC was sluggish because in
the garage temperatures could occasionally got lower than 0°C - the
lower limit of the FNDC. Whatever the cause, we decided that the FNDC
relay was not suitable for starting and stopping a generator. I ended up
re-purposing the FX's external vent fan to control the generator (and
fan) and never had any more trouble. The fan is rarely needed except
while charging batteries with the generator, and the inverter has the
ability to reduce its output if it is too hot.
Kent Osterberg
Blue Mountain Solar
On 9/14/2021 5:56 PM, William Miller wrote:
>
> Friends:
>
> A couple of years ago we installed an all sealed Outback FX system.
> All of the FX inverters were equipped with Turbo fans which connect to
> the relay in the inverters so those were not available for generator
> starting. A senior Outback tech support person (one who has been with
> Outback for a long time) told me the relay in the FNDC was not
> reliable. Instead it was suggested that I use the relay in an Outback
> Extreme charge controller that was part of the system. I never tried
> the relay in the FNDC so I don’t have first-hand knowledge if the
> relay is reliable or not. Can anyone confirm or debunk this assertion?
>
> Remember the Extreme
> <https://outbackpower.com/products/discontinued-products/discontinued-product-documentation/item/flexmax-extreme-technical-documentation>?
> It was the precursor to the FlexMax 100. It is discontinued.
>
> William
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com <http://www.millersolar.com/>
>
> CA Lic. 773985
>
> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org
> <mailto:re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf Of
> *Michael Morningstar
> *Sent:* Tuesday, September 14, 2021 11:16 AM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Radian Generator Relay
>
> Actually I’m using the 12V relay to activate a battery vent fan. For
> generator starting, I’m using the dry contact relay for two-wire
> start. I have the circuit protected by a 2amp fast acting fuse. Fuse
> is good.
>
>
>
> On Sep 14, 2021, at 11:10 AM, Tuss, Lones <lones.tuss at enersys.com
> <mailto:lones.tuss at enersys.com>> wrote:
>
> Hi Michael
>
> It sound like you are using the 12 volt aux out on the radian to
> activate a separate relay.
>
> If so disconnect the relay then check and see if the 12 aux attempts
> to go high (12v dc).
>
> If it does it may be a relay issue.
>
> The Radian does have an on board relay you could use that instead of a
> discrete relay.
>
> In AGS on the Mate3(s) just select Relay.
>
> I hope this helps sir.
>
> Take Care
>
> *From:*RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org
> <mailto:re-wrenches-bounces at lists.re-wrenches.org>>*On Behalf
> Of*Michael Morningstar
> *Sent:*Tuesday, September 14, 2021 10:55 AM
> *To:*RE-wrenches <re-wrenches at lists.re-wrenches.org
> <mailto:re-wrenches at lists.re-wrenches.org>>
> *Subject:*[RE-wrenches] Radian Generator Relay
>
>
>
>
> *CAUTION:*This email originated from outside of the Company. Do not
> click links or open attachments unless you recognize the sender and
> know the content is safe.
>
> Wrenches,
>
> I’ve got a Radian 8048/Mate 3S that no longer is activating the relay
> responsible for generator starting. I’ve power cycled everything and
> updated firmware. When I attempt to start the generator via the Mate
> 3S, the relay does not close.
>
> Any suggestions before I look into replacing the relay/board?
>
> Which board do I order and what is the best source?
>
> Many thanks,
>
> Michael
>
> *Michael Morningstar*
>
> **
>
> /Morningstar Electric/
>
> PO Box 1494
>
> Mount Shasta, California 96067
>
> 530-921-0560
>
> CSLB 949635
>
> <image001.gif>
>
>
>
> This email and any attachments may contain confidential information
> that is intended only for the recipient(s). If you have received this
> email in error, please notify the sender and delete it from your
> system. Any views or opinions presented in this email are solely those
> of the author and do not necessarily represent those of the company or
> its affiliates. This email does not constitute an agreement to conduct
> transactions by electronic means and does not create any legally
> binding contract or enforceable obligation in the absence of a fully
> signed written contract. The recipient should check this email and any
> attachments for viruses. The company accepts no liability for any loss
> or damage caused by software viruses. If you are the intended
> recipient and you do not wish to receive similar email(s) from us in
> the future then please notify the sender. Please consider the
> environment before printing.
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
> <http://re-wrenches.org/>
>
> List Address:RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>
> *Michael Morningstar*
>
> **/Morningstar Electric/
>
> PO Box 1494
>
> Mount Shasta, California 96067
>
> 530-921-0560
>
> CSLB 949635
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210914/b38841c7/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 4744 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210914/b38841c7/attachment.gif>
More information about the RE-Wrenches
mailing list