Here is our answer. The logic is not what I anticipated but it works for
me.
Interesting that there is still a need to list inverters to provide zero
backfeed current. This is necessary if you want to avoid fuses on two
string installations.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
*From:* Jeff Laughy [mailto:Jeff.Laughy at solaredge.com]
*Sent:* Friday, September 10, 2021 1:35 PM
*To:* Ryan Suchsland; Garrett Duffy; Jonathan Smith; william at millersolar.com
*Subject:* RE: [RE-wrenches] "Re-powering" Aging Utilty Scale PV systems
Hello William,
As part of the UL-1741 listing process, SolarEdge inverters are verified to
provide zero back feed current to the input source circuits
SolarEdge inverters are non-isolated, transformer-less, so the PV array
needs to operate in an ungrounded floating state. The fixed DC string
voltage for our 480 volt 3 phase inverters is 850 Vdc. Since the array is
ungrounded, the highest voltage to ground measured anywhere on the string
at the optimizer input connectors would be 425 Vdc. For this reason it is
safe to use PV modules rated at 600 volts.
Best Regards
Jeff Laughy
Principal Engineer
M +1-209-607-2402
jeff.laughy at solaredge.com
[image: cid:image001.gif at 01D495F8.2A2123F0] <https://www.solaredge.com/>
* <Emily.Welch at solaredge.com%0d# >*[image: Diagram Description
automatically generated with low confidence]
<https://www.pv-magazine.com/2021/01/21/pv-magazine-award-the-winners/>
*From:* Ryan Suchsland <Ryan.Suchsland at solaredge.com>
*Sent:* Thursday, September 9, 2021 4:50 PM
*To:* Garrett Duffy <Garrett.Duffy at solaredge.com>; Jonathan Smith <
Jonathan.Smith at solaredge.com>
*Cc:* Jeff Laughy <Jeff.Laughy at solaredge.com>
*Subject:* RE: [RE-wrenches] "Re-powering" Aging Utilty Scale PV systems
Hi all,
I had a conversation with the customer earlier basically just to address
his question, so I think it would be helpful to pull in Jeff here to help
answer the questions.
*Ryan Suchsland*
Inside Sales Account Executive
O: 510-897-8000 ext. 2180
M: 602-694-9570
Customer service & tech support 510-498-3200
ryan.suchsland at solaredge.com
<https://www.solaredge.com/>
*From:* Garrett Duffy <Garrett.Duffy at solaredge.com>
*Sent:* Thursday, September 9, 2021 12:49 PM
*To:* Ryan Suchsland <Ryan.Suchsland at solaredge.com>; Jonathan Smith <
Jonathan.Smith at solaredge.com>
*Cc:* Jeff Laughy <Jeff.Laughy at solaredge.com>
*Subject:* RE: [RE-wrenches] "Re-powering" Aging Utilty Scale PV systems
Removing customer.
Ryan / John – do we need to pull in Jeff to review this? What is the status
so we aren’t all working on this?
Thank you,
Garrett Duffy
Channel Sales Manager – Central/Midwest
Garrett.Duffy at solaredge.com
T: +1-510-552-7326
[image: id:image001.gif at 01D495F3.28951F00]
<https://nam01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.solaredge.com%2F&data=02%7C01%7C%7C69b3c107c2574a4b637008d7da76ad0c%7C6ba9fc9127b149ff8f276a548ce0b535%7C1%7C0%7C637218077379016932&sdata=o1JwBGrge5jhVMvRwUDtq77ST6h%2Fi2ZcWljw%2B9m8tes%3D&reserved=0>
*From:* William Miller <william at millersolar.com>
*Sent:* Thursday, September 9, 2021 10:05 AM
*To:* August Goers <august at luminalt.com>
*Cc:* RE-wrenches <re-wrenches at lists.re-wrenches.org>; Greg Notley <
greg at powercomengineering.com>; Jonathan Smith <Jonathan.Smith at solaredge.com>;
Ryan Suchsland <Ryan.Suchsland at solaredge.com>; Garrett Duffy <
Garrett.Duffy at solaredge.com>
*Subject:* RE: [RE-wrenches] "Re-powering" Aging Utilty Scale PV systems
August:
I am not worried about the inverter backfeeding. I only brought that up
because there was a precedent set that in order to rule out an electronic
assembly backfeeding, it had to be listed as such.
Here is what I am worried about: I am worried about the high voltage on
the output of an optimizer crossing over the optimizer in a failure
condition and energizing the input circuit of the optimizer.
If I understand the design process correctly, manufacturing to high
standards is not enough—a listing with a recognized agency to that effect
is also required.
Thanks again for thinking and writing about this. Your experience and
expertise is valued.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
<http://webdefence.global.blackspider.com/urlwrap/?q=AXicE2RkWPGcgUHuIgNDUU6loVGSXnFRmV5uYmZOcn5eSVF-jl5yfi6DoYWlh1OQaZqBmbGRsRGDe2JRUWpJiZ5LaVpapUNxfk5iUWpKeipYaUZJSYGVvn55eblebmZOTmoRWBokpc_AwDDnAgMDAGFdJb8&Z>
CA Lic. 773985
*From:* August Goers [mailto:august at luminalt.com]
*Sent:* Thursday, September 9, 2021 9:34 AM
*To:* William Miller
*Cc:* RE-wrenches; Greg Notley; jonathan.smith at solaredge.com;
ryan.s at solaredge.com; Garrett Duffy
*Subject:* Re: [RE-wrenches] "Re-powering" Aging Utilty Scale PV systems
Hi William - I think I'm picking up on a couple of separate issues here.
First, the question is whether you can install a module rated for 600 VDC
max on a 1000 VDC SolarEdge system. I realize that the article I linked to
was talking about string combiners and currents, but the isolation between
the module side and output side of the optimizer was the point. The max
input voltage on the optimizers is less than 100 VDC, so it would seem safe
to connect a module rated at 600 VDC. Keep in mind that this is just the
maximum system voltage, not the Voc, Vmp, etc. Still, I would want to
verify this with SolarEdge prior to proceeding with system design.
Your second issue related to whether the inverter will backfeed in a fault
condition is addressed in that article. I haven't done my homework to know
whether the inverter listings test for this particular fault situation. I
know that most string inverters (or maybe all?) that we've designed with
over the last 15 years say that they don't contribute reverse fault
current, so we don't count that current in our calculations for fusing. So
getting back to your question - what happens if the optimizers fail, will
modules be destroyed too? I'm sure SolarEdge's design team hopes the answer
is no. Depending on how they fail, who knows? Let's hope they are designed
and manufactured to the highest standards.
August
On Wed, Sep 8, 2021 at 11:11 PM William Miller <william at millersolar.com>
wrote:
August:
I realized I made a poor choice of words in one place below. When I wrote
“fused components” I met melted together in a heat failure, not protected
by an overcurrent fuse.
Wm
August:
Thank you for the thoughtful reply. I have come to know I can count on you
for that.
The article you site is interesting, but I do not think it applies. The
article is about current in strings, not voltages.
This interpretation of considering string currents was first introduced to
me by John Berdner (remember him?) in this article
<http://webdefence.global.blackspider.com/urlwrap/?q=AXicHYrdCcIwEIDPEVzAERKboqhPIoK--FIHkJhetHAx5S4RuosDOI5O4RrSPH4_0wm8fwCzLwDTUJmrEn6qYDty8ZE4knIxQLVaH3fNws-XtakNHCwzpqT22fthK5EsY3vDst5T6mWjdeiIkEsbvT4VPo-sG5SY2aHoTBefBUX1rQeA1wfgD-FuMew&Z>.
The John Berdner white paper is essentially the same information as in the
Solar Edge article you cited and is essential information.
What is most interesting to me in John’s article is 690.9(A) FPN. It
points out that one cannot ignore the possibility of backfeed from
inverters.
I have on occasion, when using this 690.9(A) exception to avoid combiner
fuses, been required by plan checkers to provide documentation from an
inverter manufacturer that the inverter proposed was UL certified to not be
capable of providing backfeed current. This is in spite of any intuition
that one might solidly hold that inverters can’t backfeed DC current. It’s
not true just because it seems impossible, or even if the manufacturer says
so, it’s only true if a listing agency says it is true.
The question I am asking applies to voltage isolation: If I have 850 volts
on the output of an optimizer and the optimizer fries, is there any
possibility that fused components could connect the 850 volts to the input
of the combiner? Most importantly, does a listing agency say it is not
possible? If it is not certified, then using optimizers is not a design
option.
Three persons from Solar Edge have told me the isolation is infallible.
I’m not trying to be difficult, but I really think this assertion has to
confirmed by a listing agency. I have not seen that yet.
Solar Edge has been quick to reply to my voicemails and has expressed a
real interest in this project, much to their credit. I will press this
point to them and I will post to this forum what I learn.
By the way, I am sure you have not forgotten a recent flurry of posts on
this site recently about rapid shut down device(s) frying in use.
Optimizers are similar devices in the same demanding environment and
exposed to high voltages as well. Equipment failure is always a
possibility.
Thanks again to those many participants who have replied to my question. I
am much smarter because of my wrench forum friends.
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
<http://webdefence.global.blackspider.com/urlwrap/?q=AXicE2RkWPGcgUHuIgNDUU6loVGSXnFRmV5uYmZOcn5eSVF-jl5yfi6DoYWlh1OQaZqBmbGRsRGDe2JRUWpJiZ5LaVpapUNxfk5iUWpKeipYaUZJSYGVvn55eblebmZOTmoRWBokpc_AwDDnAgMDAGFdJb8&Z>
CA Lic. 773985
*From:* August Goers [mailto:august at luminalt.com]
*Sent:* Wednesday, September 8, 2021 4:44 PM
*To:* William Miller; RE-wrenches
*Subject:* Re: [RE-wrenches] "Re-powering" Aging Utilty Scale PV systems
Hi William - You raise a great question - can you install 600 VDC modules
on a 1000 VDC SolarEdge system? Of course the DC optimizer output circuit
would need to be rewired with 1000 VDC wiring and connectors, but I think
the answer is "yes." According to this article
<https://www.solaredge.com/sites/default/files/application_notes_string_combiners_na.pdf>,
"In a SolarEdge system, the PV modules are isolated from the DC output
circuit by the power optimizer." To me, it sounds like there is no risk of
going over the max optimizer input voltage. I would want to verify this
with SolarEdge prior to designing any systems, but it seems like a good
idea to explore!
I was recently on another group chat, and someone mentioned being in a
similar predicament to you. They want to upgrade an old central inverter.
Anyway, they had found that the SMA CORE1 33 kW unit at least can be strung
up to work with 600 VDC modules and wiring:
https://files.sma.de/downloads/STPCORE1-DS-en-28.pdf?_ga=2.30799225.717469396.1631144387-1894865662.1631144383
<http://webdefence.global.blackspider.com/urlwrap/?q=AXicRc5NDgExGIDhzxFcwA3mm2k705lKhPgJO4K9lLZIOlNpi7iLAzgOp3ANYmP75lm87RY83gCdF4C3N0K3GPwFa3m0O9dE7yzuXA2kErPhsjAZZ5RRmErvdYw4PhtzGwRnpddqr3_0EOMpdNPUHK0OGGqJSqfKXRvrpArpar0YzZcTkoxXiW4SWuFJmf5mL3sUWVYKQWmBJSlzLpjgSDgjJM9ZVSbfh7ziBef0XxkA3J8AHzTCOXU&Z>
I'm sure you'd have to redo a lot of the conduit and wire to accommodate
several smaller inverters, but this might be worth exploring as well.
August
Luminalt
On Wed, Sep 8, 2021 at 4:13 PM William Miller <william at millersolar.com>
wrote:
Friends:
I learned a new buzzword recently: “Re-powering.” It means replacing
inverters on an existing PV system of ten or more years old. Due to the
high number of systems of this vintage it appears that re-powering has
become somewhat of a sub-industry. The big problem is these systems are
all 600 Volt limited PV panels, combiners and re-combiners and there are
no 600 volt utility grade inverters being manufactured.
I am working on a utility scale system
<http://webdefence.global.blackspider.com/urlwrap/?q=AXicZYpRDgExFEWfJdiAJbSmE4IvQcKPRLCBqtY0Xj15fSSzFwuwHFZhGzLzJfF3zzm324HnB6D3BmCsC3NQme8q2YiOLsKEylGCYjRezbaD0B-WpjSwtMxeRC1uIdTTTGjZH0--vVYi1zzROkVEz21rvF63vGtYb4glEEbSc0rJs4sWf-aerTt7_jeqkoQA8HgBfAHT5UDu&Z>
built about 14 years ago that fits the description above. There are two
250KVA Xantrex GT250 inverters and one has failed. The question of the
moment is: Repair or replace?
Repair: If we fix these inverters, can we count on support in the future?
We can negotiate a service contract with Schneider at a cost yet to be
revealed. This requires we buy a spare parts kit for about $100K. There
are a few other companies that claim to offer repair services on these
inverters but none has followed through.
Replace: The PV plant is built with panels and BOS all limited to 600 VDC
max. There are no more 600 volt input utility scale inverters being built,
or at least none that I have found. If we install a 1000 or 1500 volt
inverter we may have to replace the entire PV array and BOS. It may be
possible to convert the output of the existing panels to a higher voltage
with DC-DC converters.
Here are the options I see:
Optimizers: One purveyor of optimizers is Solar Edge. Solar Edge offers a
100 KVA inverter. This inverter requires DC input of 850 volts. The
inverter requires optimizers to obtain this voltage. The question: Do the
optimizers isolate the PV from the higher string voltages in the case of a
catastrophic failure of one or more of the optimizers?
Repower with outboard DC-DC voltage converters, such as provided by Alencon
Systems. Solectria has successfully done this. Here
<http://webdefence.global.blackspider.com/urlwrap/?q=AXicHYzLDcIwDEDNCCzABkloKxD0hBASnNkgFKeNlE9lm6LuwgCMA1OwBoXz-8xn8PwALN4AFMaivGimQUfrQ5OTUA66yRGKzfa0P6_ccl2VVQlHS4Qi-nBzbtxxDpbw2uJf7UR6ro2xAdO04JEFI_-QCWgp-dSaflBTT9l5YXX30ikhm9hlikgBmZVPA5IgsQGAxwvgC8UeOyM&Z>
is a paper on the subject.
If anyone has dealt with this issue before I would sure appreciate any
wisdom.
Here is a link
<http://webdefence.global.blackspider.com/urlwrap/?q=AXicLYrbCcJAEEXHEmzADrKbB4r6JSLojyCxAFnjJFmYzYbZiZJeLMBytArbkAT_zjn3Tifw-gLMPgBMfZJeVeC7csZS4RthT6rwDpLl6rDN52W8yNIshb1hRhG168qy3wRPhvFW4XitRdqw1tpZIuRxG7o-jn4eXBcm4CVId7MYdBZHOUYn_0C2TaUZo_bPqhZHAPB8A_wAixU5nw&Z>
to a web-page I built for this project.
Thanks,
William Miller
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
<http://webdefence.global.blackspider.com/urlwrap/?q=AXicE2RkWPGcgUHuIgNDUU6loVGSXnFRmV5uYmZOcn5eSVF-jl5yfi6DoYWlh1OQaZqBmbGRsRGDe2JRUWpJiZ5LaVpapUNxfk5iUWpKeipYaUZJSYGVvn55eblebmZOTmoRWBokpc_AwDDnAgMDAGFdJb8&Z>
CA Lic. 773985
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
<http://webdefence.global.blackspider.com/urlwrap/?q=AXicE2RkWPGcgUHuIgNDUU6loVGSXnFRmV5uYmZOcn5eSVF-jl5yfi6DoYWlh1OQaZqBmbGRsRGDe2JRUWpJiZ5LaVpapUNxfk5iUWpKeipYaUZJSYGVvn5Rqm55UWpeckZqsV5-UToDA8OcCwwMAJ4uI8M&Z>
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
<http://webdefence.global.blackspider.com/urlwrap/?q=AXicXcrRCcIwEADQAydwATfoxaYo2i8RQb_dIMYkDaS5cjmV7uIAjqNTuIbgl_j93nQCjzfA7AXAaaz1CQtfsTcxWcrClNBSD_VqfdgeF36-bHSjYW-YnQjuLt6Pm0LJsDsH962dyNAqlWKRguyqG7tsO1eQOCgaJFIuaENUP1b9PQC4PwE-43Q1Vg&Z>
There are two list archives for searching. When one doesn't work, try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
<http://webdefence.global.blackspider.com/urlwrap/?q=AXicE2RkWPGcgUHuIgNDUU6loVGSXnFRmV5uYmZOcn5eSVF-jl5yfi6DoYWlh1OQaZqBmbGRsRGDe2JRUWpJiZ5LaVpapUNxfk5iUWpKeipYaUZJSUGxlb5-eXk52BjdxKLkjMwysKR-UapueVFqXnJGarFDTmZxSbEekoheflG6PgMDw5wLDAwA06AzRg&Z>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
<http://webdefence.global.blackspider.com/urlwrap/?q=AXicE2RmWPGcgUHuIgNDUU6loVGSXnFRmV5uYmZOcn5eSVF-jl5yfi6DoYWlh1OQaZqBmbGRsRGDe2JRUWpJiZ5LaVpapUNxfk5iUWpKeipYaUZJSYGVvn5OZnFJsV5Rqm55UWpeckZqsV5-Ubp-QWZBahHIcH0kGV00VQwMDHMuMDAAAHnsNKw&Z>
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
<http://webdefence.global.blackspider.com/urlwrap/?q=AXicHcvRDcIgEADQcwQXcAMPS6PRfhljot9ugHiUJlD0uEq6iwM4jk7hGhr_35tO4PkBmL0BOIyVPmPmO0bTBZt64RTQpgjVenPcnZZusap1reFgmEkE94Nz4zanYJguLf2pF7k2SpVSkGlemHrrKWPiVpF0t-H3CL1EAHi8AL59FSrW&Z>
Check out or update participant bios:
http://www.members.re-wrenches.org
<http://webdefence.global.blackspider.com/urlwrap/?q=AXicE2RkWPGcgUHuIgNDUU6loVGSXnFRmV5uYmZOcn5eSVF-jl5yfi6DoYWlh1OQaZqBmbGRsRGDe2JRUWpJiZ5LaVpapUNxfk5iUWpKeipYaUZJSYGVvn55eblebmpuUmpRsV5Rqm55UWpeckZqsV5-UToDA8OcCwwMAHqSKG8&Z>
Click here <https://www.mailcontrol.com/sr/MZbqvYs5QwJvpeaetUwhCQ==> to
report this email as spam.
This message has been scanned for malware by Websense. www.websense.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210910/40b7b124/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 12268 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210910/40b7b124/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 1807 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210910/40b7b124/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.gif
Type: image/gif
Size: 1449 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210910/40b7b124/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1809 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210910/40b7b124/attachment-0002.jpg>
More information about the RE-Wrenches
mailing list