Rebekah:



Thanks for your help with this.



Because I snapped up all of the 100 series rack I could (pun intended), I
am past the recertification with newer modules.  My argument is that
although the rail was discontinued, the clips remain.  What  I did is
extracted a page from the UR series manual showing testing with the Mission
panels and inserted it into the permit set.  I hope this sleight of hand
passes plan check.



William Miller



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *Rebekah Hren
*Sent:* Tuesday, July 20, 2021 6:20 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Snap-n-rack bonding certification



Minor update, I got word from Snapnrack that: "The new protocol established
with UL eliminates the need to include the wattage ranges for each module
type"

Still a pain and the manufacturer/model should be on the rack manufacturer
list - but not down to the precise wattage -  so slightly less of a pain.



Rebekah

Tel: 336.266.8800





On Tue, Jul 20, 2021 at 4:37 PM Rebekah Hren <rebekah.hren at gmail.com> wrote:

Hi William



Groan, I don't see that precise model in the series 100 installation manual
<https://snapnrack.com/wp-content/uploads/2019/05/S100-UL-Install-Manual_v2.0_web.pdf>
on
pg 74 which is the bonding evaluation list of modules

I hope for your sake Snapnrack will send an email the AHJ will accept that
includes that module.

I wish there was a reasonable workaround for AHJs here, like onsite
resistance measurements.



Good luck,

Rebekah

Tel: 336.266.8800





On Tue, Jul 20, 2021 at 2:36 PM Sam Haraldson <sam at onsiteenergyinc.com>
wrote:

The SnapNrack UL 2703 document highlights it's UL listing when used with
Type 1 and Type 2 modules.

https://snapnrack.com/wp-content/uploads/2019/05/SnapNrack_Fire_Classification_Tech_Bulletin_v.2-1.pdf

*SnapNrack Series 100, Ultra Rail and RL systems have been Certified for a
Class A fire rating with Type 1 and Type 2 modules, in accordance with the
standards set forth in UL1703/2703 and IBC 2012.*



The Mission Spec sheet references that it is UL listed under 1703.

https://s3.amazonaws.com/ecodirect_docs/Mission-Solar/Mission-Solar-MSE320SR8T-datasheet.pdf



For further reference this 1703 document talks a little about the different
module "types" that are tested.

https://www.intertek.com/building/standards/ul-1703/

*The “Type” of module dictates the number of fire tests that will be
required during the test process, there are 3 common types (15 total) that
are determined by their superstrate, encapsulant, substrate materials, and
size of module.*





*Sam Haraldson <sam at onsiteenergyinc.com>*

Installation & Service Manager

<http://www.onsiteenergyinc.com/>

|

o. (406) 551-6135

<https://www.facebook.com/onsiteenergysolar/>

<https://www.instagram.com/onsiteenergyinc/>

<https://twitter.com/onsiteenergyinc>

<https://www.linkedin.com/company/onsite-energy-inc/>

<https://onsiteenergyinc.com/bcorp>





On Tue, Jul 20, 2021 at 3:25 PM William Miller <william at millersolar.com>
wrote:

Friends:



I received the following correction noticed from a hired plan-checker:



*Please provide the technical listing for the support rail system
documenting that the supports have been tested with the PERC 60 panels. The
UL 2703 listing requires the two to be tested/listed together for the rack
to functionally ground the solar panels. [CEC 690.43(A)] Alternately, bond
the metal parts of PV equipment to grounded metal supports per CEC
690.43(B).*



Is it true that UL2703 requires testing with each and every type of module?
I am using 100 Series rail from my stock with Mission MSE325SR8K panels.
Does anyone have any documentation on file that would satisfy this request?



I have sent an inquiry to Snap-n-rack about this but they often take a week
or more to respond.



Thanks in advance.



William Miller



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210720/8a54162e/attachment.htm>


More information about the RE-Wrenches mailing list