HI Kirpal,

This sure seems like a real possibility.  

I don’t know that there have been any firmware updates.  I know its one REV behind, but tech support didn’t think that was an issue.  

As to the installer menu, does anyone know where I can find a map/menu of all the options?

thx

jay

> On Jul 18, 2021, at 7:46 PM, Kirpal <solarworks at gmail.com> wrote:
> 
> Hi Jay.  We had a similar situation arise once after we updated the firmware of a 4048 radian.  The inverter was a circa 2015 unit.  After updating it would only sell about 1/4 of the normal array output to the grid.  
> We talked to Chris at tech support and he had us go into the installer menu and look up the max sell current and somehow the inverter firmware update had changed a setting deep in the installer menu to limit sell amps.  It was a menu which we had never been in.  Adjusting to the normal 16a of sell current up from the 4A immediately corrected the issue.  
> Your problem sounds exactly like the one we experienced. 
> Did you update firmware recently?
> I believe you have to be on site to access the installer menu....
> Chris is typically on the job at 6am pacific time and easy to get ahold of early....I recommend trying to get ahold of him to walk you thru the steps.  
> Best of luck.
> Kirpal 
> Oregon Solarworks 
> 
> 
> On Sun, Jul 18, 2021, 12:26 PM jay <jay.peltz at gmail.com <mailto:jay.peltz at gmail.com>> wrote:
> HI All,
> 
> I”m trying to diagnose the following system I didn’t install.
> 
> 4 year old system grid tie battery back up.
> 
> Radian 4048
> flexmax 80
> 3500 watts PV
> fndc
> it is on opticsRE
> 
> The symptoms are that its not selling much at all.  Mostly when it is about 1kw max PV production and .8kw selling.  I have disconnected the FNDC and after that it did seem to work better.  
> 
> Usually it will sell a bit, then buy a bit then sell and so on.  Grid voltage is very constant at around 246vac. 
> 
> I’ve been through the settings a few times with tech support, made adjustments and for a while it was selling pretty normally, but again today 0 production, CC is at float.  
> 
> I have not been to the site, I was just trying to do this all by optics.  But I’m going to have to go.   I think there are 3 possible issues.  
> 
> 1. the customer has always thought the production is low.  And from what I’ve seen that is true.  This is in a very sunny place, no shade so with 3.5kw, 1kw is very low which I think they may have  a few strings of the array are not connected. However why that bothers me is that the VOC/VMP voltages are too close in looking at the CC.  Which leads me to think its been told to back off to the 1.0kw, by some setting, see #2. And its always around .8 selling and around 1kw output from the array. 
> 
> 2.  There is a programing issue.  
> 
> 3. There is a hardware issue.
> 
> 
> If someone wants to look at the site, I have the info and they can log in.  
> Or if they want to provide settings for me to triple check, that would be great
> and 
> if they have any ideas as to why its acting like it is, very much appreciated 
> So far even though tech support has viewed in on Optics and have had some recommendations as to settings, its not fixed the issue.
> 
> thanks in advance,
> 
> jay
> 
> peltz power
> 
> 
> 
> 
> 
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>
> 
> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210718/12c29ba1/attachment.htm>


More information about the RE-Wrenches mailing list