[RE-wrenches] XW PRO/AC Hydro
jay
jay.peltz at gmail.com
Wed Jun 30 08:50:46 EDT 2021
HI All
I”ve worked with many high voltage AC hydros and a few AC direct. Having a 2kw one is really small, and I can see why there were issues.
I recommend doing it this way,.
1. install a XW 600v controller.
2. take the output of the hydro after all safety/regulation controls and rectify it and feed it into the CC.
3. set the CC max charge rate to a bit below the output of the hydro. That way the hydro regulation will work normally.
As the hydro output lowers due to lower water flows, you will have to adjust the CC output. With an AC direct hydro there is usually a failsafe device which interrupts the water flow ( flow diverter) if the HZ get too low, so you really don’t want that to happen.
My concern with going through the inverter as the charger is much lower efficiency and its not as fine adjustment as the CC leading to lower outputs and more potential issues.
4. The xanbus /battery will comm with the CC for regulation, as it turns down the CC, the hydro regulation will reduce output with its dump loads, all normal.
5. and it leaves both inverters for normal use.
jay
peltz power
> On Jun 29, 2021, at 5:40 PM, Jerry Shafer <jerrysgarage01 at gmail.com> wrote:
>
> I bet if you thought a little harder, you could get it even more complicated. If the hydro has both freq and voltage control then look at a dumb charger. Keeping it all independent will be safest. On the other hand l used an outback and connected a wind turbine to the AC in and the inverter just used it first. I set the max input amps and it worked and the inverter picked up the rest, l did have a water heater as a dump and it would pop the t&p sometimes. I dont know how well if at all the voltage is regulated on your controller and It can get complicated.
> Jerry
>
> On Tue, Jun 29, 2021, 12:49 PM Michael Morningstar <mjmorningstar at gmail.com <mailto:mjmorningstar at gmail.com>> wrote:
> Will this work?
>
> A friend has an off-grid property that is served by a Canyon Industries AC turbine w/ T&H controller. Output is around 2kw. Of course, no surge capacity there. He has recently moved there full time and is Vrbo’ing one of the cabins so power needs have increased.
>
> What I have done previously in these situations with low Kw AC turbines is install a battery based system and Iota chargers that are powered from the turbine. That’s always worked well, BUT now that we are disciples of the Discover AES/XW pairing I thought I would try this:
>
> 1) Connect the turbine’s output to AC2 and use Gen Support to enable loads above 2kw or surges. That’s placing a lot of faith in Gen Support, and if it were to not respond quick enough, well …trouble. The site is six hours away.
>
> Then my friend tells me that he would like to throttle the turbine down during the summer to conserve water, reducing output to .5-1kw. So, I got to thinking:
>
> 2) One inverter for charging only. One inverter for power output only. Charging inverter communicates with AES through Xanbus and is connected to a Gateway/Insight so that I can remotely adjust AC2 input current to scale with seasonal turbine fluctuations. Neither inverter is Synced or knows of the other’s existence. Output inverter gets a SCP for basic control and monitoring. Battery bank is connected to a Discover SOC monitor.
>
> I guess my questions are: Do you see any problems with this arrangement? Would having what amounts to an external load (the output generator) trip things up since it’s not communicating w/ the batteries? Could/Should I include the output inverter in the Xanbus loop? And/Or can I connect the output inverter to the Gateway device since it has two inputs,
> Xanbus 1 and 2.
>
> I’ve tried to reach Schneider to speak about this to no avail. Great product, not so great support.
>
> Thanks in Advance,
> Michael
>
>
>
>
> Michael Morningstar
>
> Morningstar Electric
> PO Box 1494
> Mount Shasta, California 96067
> 530-921-0560
> CSLB 949635
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>
>
> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>
> <SmallGif.gif>_______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210630/83eab22b/attachment.htm>
More information about the RE-Wrenches
mailing list