[RE-wrenches] 2000v DLO/RHW-2 : in conduit required?

Ray ray at solarray.com
Sat Jun 5 16:43:11 EDT 2021


I brought this very question up a couple of years ago here. IMHO, it 
needs to be in conduit.  I have not found NEC exemptions for DC battery 
cable.  We modded the cabinet, so that we could put a 2" KO on the side, 
and ran conduit straight to it.  Everything is accessible from the top 
and front, so I don't see the need to having it roll away from the wall. 
We ended up also relocating the buss block inside, because it was really 
hard to get to, to torque the connections.  I can share our mods, if 
you're interested.


Ray Walters
Remote Solar
303 505-8760

On 6/5/21 1:41 PM, Kirk Herander, VSE wrote:
> Hello All,
> I've now done several Blue Ion, both 48vdc and HV storage systems. 
> Those with experience know that the 2.0 cabinet DC cabling comes out 
> the back of the unit. In my 48v off-grid installs I've used DLO/RHW-2 
> into a wireway, making a DC bus with power distribution blocks, then 
> to inverter, etc. I loop and support the cable from the back of the 
> battery cabinet, allowing extra should I ever need to move it(it's on 
> casters) to access the back for servicing.
>
> The current BI 48v system I am building is commercial grid-tie and 
> requires AHJ inspection. Is having RHW-2 cable in free air from the 
> cabinet to a wireway NEC-legal (i.e. without conduit)? Obviously if 
> conduit is needed, it eliminates looping and an easy roll of the 
> cabinets away from a wall for service.
>
> Thanks. I await the opinion of of the BI gurus of this forum. Found 
> references on Mike Holt's forum to DLO/RHW-2 and conduit requirement, 
> but no consensus one way or the other.
>
> *Kirk Herander / **kirkh at vermont.solar <mailto:kirkh at vermont.solar>*
>
> *Owner|Principal, VT Solar, LLC*
>
> */Celebrating our 30^th  Anniversary 1991-2021!!/*
>
> *www.vermont.solar* 
> <https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0>**
>
> dba Vermont Solar Engineering
>
> 802.863.1202
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210605/56103ff1/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: akalfolpjolgfckl.jpg
Type: image/jpeg
Size: 163485 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210605/56103ff1/attachment.jpg>


More information about the RE-Wrenches mailing list