My real world input is I use the XW for anything hard to start.
XW is a single 6.8KW low frequency design that can supply 12KW for a
minute. Radian is (2) 4KW inverters and I have found that XW is the best
for this. Stacking often is not the answer for difficult loads. My
experience only with deep wells offgrid!
I use Radian also but not for something like this!
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridsolar at sti.net
text 209 813 0060
On Tue, 25 May 2021 08:50:24 -0700, frenergy <frenergy at psln.com> wrote:
> I need some actual off-grid experience some of you wrenches may have had
> with with a (or 2) Radian(s) starting and running a 3HP, 230Volt, single
> phase, 3-wire submersible well pump. It would be starting against a
> 50-100 foot static level in the well and a pressure in the pressure tank
> of 35psi.
>
> Yesterday I clamped a 2 HP well pump and during start up
> got an inrush current on a Fluke of 38 amps (both legs), which was
> against 200 feet of water column and 40psi in the tank. Unfortunately, I
> need a 3HP pump for this install. I've read specs on all sorts of data
> sheets, running amps, max amps,locked rotor amps, but I need real world
> knowledge. What do we know?
>
> Bill
>
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049
> www.frenergy.net
More information about the RE-Wrenches