[RE-wrenches] SMA SB 2500U

Jerry Shafer jerrysgarage01 at gmail.com
Tue May 18 21:22:59 EDT 2021


Wrenches
I would also be surprised if the old 2500 would last very long.
Better off with a SB5.0-41 and if you need RSD then add that in also.

On Tue, May 18, 2021, 12:15 PM Dave Angelini Offgrid Solar <
offgridsolar at sti.net> wrote:

> Probably if it is old it does not have these recent Certifications and UL
> requirements. Just gave these to my local AHJ.
>
> IEEE 1547, UL 1741-SA, Rule 21, Rule 14H, PREPA, and CSA 107.1
>
> Product Certification History Project Date Description 80049402 2020-09-18
> Update to report 70194014 to meet grid support function according to CA
> Rule 21 for 120Vac output configuration. 80036281 2020-03-15 Update report
> 70194014 to include UL1741 CRD SA17/18 UL 1741(California Rule 21 Phase 3
> Function 2 and Function 3) for Model XW Pro 6848 NA. 80020062 2019-10-30
> Update report 70194014 to include firmware upgrade for Model XW Pro 6848
> NA. 70220117 2019-03-27 Update Report 70194014 to include minor firmware
> update for Model XW Pro 6848 NA. 70212688 2019-03-04 Update Report 70194014
> to Include Volt-Watt and revised Freq-Watt grid tie requirements as per
> UL1741 Supplement SA for Model XW Pro 6848 NA (FGA 865-6848-21).
>
> *Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/>
> e-mail  offgridsolar at sti.net <offgridsolar at sti.net>
> text 209 813 0060*
>
> On Tue, 18 May 2021 14:07:08 -0400, "Glenn Burt" <glenn.burt at glbcc.com>
> wrote:
>
> Hi Kirk,
>
>
>
> Can you elaborate on which UL standards the older SB units don't comply
> with?
>
>
>
> -Glenn
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Kirk Herander, VSE
> *Sent:* Tuesday, May 18, 2021 6:42 AM
> *To:* re-wrenches at lists.re-wrenches.org
> *Subject:* Re: [RE-wrenches] SMA SB 2500U
>
>
>
> These older Sunnyboys do not comply with latest UL standards regardless.
> If its a new installation, a savvy utility  / AHJ will catch this.
>
>
>
> *Kirk Herander / kirkh at vermont.solar <kirkh at vermont.solar>*
>
> *Owner|Principal, VT Solar, LLC*
>
> *Celebrating our 30th Anniversary 1991-2021!!*
>
> *www.vermont.solar*
> <https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0>
>
> dba Vermont Solar Engineering
>
> 802.863.1202
>
> On 5/17/2021 3:53:26 PM, William Miller <william at millersolar.com> wrote:
>
> Jay:
>
> Some years ago I mis-ordered 5 SB2500s for 208 three phase and it turned
> out the system was 240 VAC three phase (open delta). I had to return the
> inverters to the factory to be converted and I had to rewire all of the
> arrays. So no, I don't think this can be done in the field.
>
> William Miller
>
> Miller Solar
> 17395 Oak Road, Atascadero, CA 93422
> 805-438-5600
> www.millersolar.com
> CA Lic. 773985
>
>
> -----Original Message-----
> From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org
> <re-wrenches-bounces at lists.re-wrenches.org>] On
> Behalf Of Jay
> Sent: Monday, May 17, 2021 11:44 AM
> To: RE-wrenches
> Subject: [RE-wrenches] SMA SB 2500U
>
> Does anyone know if you can convert a
> SMA SB2500U ( old red inverter) from 208 to 240vac?
>
> Without using a boost transformer.
>
> Thx
> Jay
>
> Peltz power.
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210518/53a1546a/attachment.htm>


More information about the RE-Wrenches mailing list