Kirk,
Could there be a loose wire connection to the breaker? That could cause it
to heat up an trip sooner than it otherwise would.
Cheers,
Dave

On Sat, May 8, 2021, 2:13 PM Kirk Herander, VSE <kirkh at vermont.solar> wrote:

> I have a system where the SE10000 inverter fried internally. The 60A AC
> output breaker tripped several times, as a result of the homeowner
> resetting over and over until he called me.
> I replaced the inverter under warranty and all is fine, except on sunny
> days the breaker will trip at about 40A, close to the max output of the
> inverter. Reset it outside of peak inverter output and its good. I assume
> the breaker has weakened from stress of some sort, so I replaced it and
> time will tell.
> Anyone ever seen a breaker have it's trip point reduced like this?
>
> *Kirk Herander / **kirkh at vermont.solar <kirkh at vermont.solar>*
>
> *Owner|Principal, VT Solar, LLC*
>
> *Celebrating our 30th Anniversary 1991-2021!!*
>
> *www.vermont.solar*
> <https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0>
>
> dba Vermont Solar Engineering
>
> 802.863.1202
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210508/fcdf14de/attachment.htm>


More information about the RE-Wrenches mailing list