[RE-wrenches] NEC 690.8(A) - Bifacial Modules
Steven Lawrence
lawrencesteven at gmail.com
Wed Mar 17 09:18:36 EDT 2021
Hi Corey,
I start off by using the BSTC value as the baseline Isc before I do the
classic 1.25x1.25 multiplication. It does end up causing larger currents
and oversizing the wire. Most of the time our projects have a strict DC
Vdrop requirement so we're always oversizing the wire anyway, so it's not a
big deal. However, for the Neher-McGrath calculations, I will typically
run a SAM model and re-calculate the ISC that way (on 100kW and larger
projects only). I base this off the SolarPro article from a few years back
where you calculate Isc0 using nameplate Isc, cell temperature, irradiance,
and the module current coefficient. For the irradiance, I use the front
side POA and the anti-POA multiplied by the bifaciality factor - usually
70%.
My last run had a situation where SAM was calculating a higher Isc value
than the Isc0 equation value, so I will probably end up using that. It is,
however, less than the traditional BSTC nameplate x 1.25 method.
Regards
Steven Lawrence, PE