On both Outback and Midnites's AC/DC Load centers, they just have 
separate areas, but there is no partition, or anything like that. They 
are UL listed.  I don't do GT, so I don't really deal with this issue 
outside of the E panel, but if it were me, I'd just zip tie the PV wires 
together, put labeling on them so that it was clear they were PV 
conductors, and call it a day.

Ray Walters
Remote Solar
303 505-8760

On 2/1/21 6:55 PM, Dave Angelini Offgrid Solar wrote:
>
> I land 600vdc PV into the Mppt/Mppt's only.  I never mix 600vdc with 
> anything except SPD/disco ever!
>
> Just not that hard and for offgrid, standard practice for reliability. 
> Same with 150vdc, I never get it into the PDP and disco it up stream 
> form mppt.
>
>   
> *Dave Angelini Offgrid Solar "we go where powerlines don't" 
> http://members.sti.net/offgridsolar/ 
> <http://members.sti.net/offgridsolar/> e-mail offgridsolar at sti.net 
> <mailto:offgridsolar at sti.net> text 209 813 0060*
>
> On Mon, 1 Feb 2021 15:37:34 -0700, Mac Lewis <maclewis1 at gmail.com> wrote:
>
>> Hello wrenches,
>> What are folks using for raceway partitions to comply with 690.31(B) 
>> when running AC/DC and batteries conductors through a common gutter?  
>> Is there a product or just something made by the installer?  These 
>> multiport inverters make it difficult not to use a gutter and have a 
>> clean installation.
>> Thanks!
>> -- 
>> Mac Lewis
>>
>> "Yo solo sé que no sé nada." -Sócrates
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210201/f36d29d1/attachment.htm>


More information about the RE-Wrenches mailing list