[RE-wrenches] Radian Charges 1 hour per calendar day

Ray ray at solarray.com
Fri Jan 8 18:03:52 EST 2021


I agree with William, SOC is just a calculation, that can change with 
temperature, age of batteries, and even when the last full charge 
occurred. We just had trouble with an inherited Sunny Island system that 
only allows gen start settings based on SOC. The actual battery SOC 
didn't correspond to the programming after a while, and the dumb thing 
would shut off due to low voltage, BEFORE starting the generator.  Then 
being AC coupled, you also have disabled the PV charging source.  
Triggering gen start off SOC and having your array AC coupled is a 
RECIPE for disaster, speaking of Cooks in the Kitchen, William.

   Ray Walters

Remote Solar
303 505-8760

On 1/8/21 4:24 PM, William Miller wrote:
>
> Mick:
>
> Here’s a thought:  If the system has an FNDC, the charging may be 
> programmed to terminate at a specific SOC.  I have been told by OB 
> tech support, and I believe this, that using SOC and battery voltage 
> over time and/or charge taper to control charging is like the old 
> adage, “too many cooks.”
>
> My understanding is the best parameter for terminating an absorption 
> charge is charge taper, if your system has this option.  Taper is the 
> best indication of complete charging. This is typically set at 3% of 
> the 20 hour AH rating.  All other charge termination options should be 
> disabled.
>
> Too many charge termination “cooks” may be the cause of your problem, 
> Mick and the problem Drake posted I believe just today.
>
> I have been meaning to write some thoughts on the very concept of 
> SOC.  As I understand it, SOC is a calculated value, using AH in 
> versus AH out and adjusted for charging efficiency.  I believe this 
> process has a high probability for inaccuracy because the actual 
> efficiency value is a moving target.  It changes with temperature, 
> battery charge state, battery age and probably other factors.  This 
> belief is reinforced by the fact all of these SOC measuring systems 
> must have a built in recalibration that typically occurs when some 
> voltage over time condition is met.  The default values for this reset 
> to 100% SOC are deliberately too low to ensure calibration actually 
> occurs, but it gives clients an inaccurate impression of when battery 
> charging is fully accomplished.
>
> Way too often I have seen clients manually terminate generator 
> charging of a battery bank prematurely because they see the SOC is 
> 100% and yet their generator is still consuming fuel and making noise, 
> something they do not want to occur unless they know it is required.  
> This means batteries do not get the absorption time they need for a 
> long life span.
>
> I have contemplated discontinuing installation of FNDC units for this 
> reason.  In fact, the only benefit I see to an FNDC unit is to allow 
> battery parameter logging.  I tell my client to ignore any number 
> followed by a % sign.  I am BCC-ing several clients on this post 
> because I want them to have more background on why I say this.
>
> I am interested in what others think about the benefit, or lack 
> thereof, of using derived SOC values.
>
> William
>
> PS: I would not assume a recently purchased system has the latest 
> firmware.
>
> Wm
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com <http://www.millersolar.com/>
>
> CA Lic. 773985
>
> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org 
> <mailto:re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf Of 
> *Mick Abraham
> *Sent:* Friday, January 8, 2021 12:46 PM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] Radian Charges 1 hour per calendar day
>
> Happy Friday, Mechanix~
>
> Drake Chamberlin wrote about the Radian inverter that began running a 
> "too short" absorption interval after several years of normal 
> operations. Drake said the possible culprit is inverter firmware per 
> Outback; I wish to add a data point & follow up questions:
>
> I sold an Outback SE-830BLU-300AFCI Systemedge Package--which includes 
> Outback batteries & all for quick deployment--to a longtime retail 
> client in the Autumn of 2020. Firmware seems likely to be the latest 
> version on all components since it shipped from OB so recently. The 
> client's internet service to the site was lost along with everything 
> else in a CA wildfire--so I can't look in remotely & I can't 
> physically travel to the site. He has much prior experience with 
> inverter/chargers, off grid living etc. but he's new to the Radian, 
> Mate3s, etc.
>
> My off grid client reports his new Radian is shifting to float before 
> the Absorption target voltage is even reached & the shift occurs 
> around 56.1 volts battery voltage on the way up. The battery is cool, 
> not warm. He's been through the menus & couldn't find a likely suspect 
> for this behavior. The FM100 PV controller on the same system is able 
> to push the battery to the absorption target then hang there as would 
> be expected before it shifts to float. That's if the daylight lasts 
> long enough, of course. As with Drake's client, my friend needs to be 
> able to pump the battery to a higher state of charge with his 
> generator than what he's getting. His upscale (but lead acid) Outback 
> BLU batteries we bought in the package seem at risk of harm due to 
> this problem--& I'm sure Drake has similar concerns. I asked the 
> client to reboot the generator AC (breaker off, then back on) to see 
> if he could push the battery closer to the absorb voltage that way but 
> I am still waiting for that answer.
>
> Thanks to the clues & cues from Drake, I'll cut & paste this into a 
> trouble ticket with OB. While waiting for that to percolate through 
> the system, here's one more question for the hive mind:
>
> * When a Systemedge Package is purchased complete with batteries & 
> all, are the chargers & the FNDC battery monitor already 
> pre-programmed for the battery type & size? Here's hoping, and as 
> always, the Wrench List is the Bomb!
>
> Mick Abraham, Proprietor
>
> www.abrahamsolar.com <http://www.abrahamsolar.com>
>
> Landline: 970-731-4675
>
> Cell phone or for text messaging: 970-946-6584
>
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20210108/7b48713b/attachment.htm>


More information about the RE-Wrenches mailing list