[RE-wrenches] generator tripping GFCI
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Sun Dec 20 11:52:25 EST 2020
One way to troubleshoot this is by elimination. The genset would be a
start. The GFCI itself. I have had to switch from the contractor grade GFCI
to a quality make in new construction.
Since this is new I would make
sure on the AC panel, critical loads like the house pump or fire pumps and
refrigerator/ freezer were NOT put on GFCI. I have seen some very bad
things happen from this circuit that have nothing to do with ground faults.
The same for AFCI or my guaranteed income source from grid-tie
inverters.
Dave Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/
e-mail
offgridsolar at sti.net
text 209 813 0060
On Sat, 19 Dec 2020 15:33:36 -0700,
jay wrote:
> HI All,
>
> I have a client with a older Kohler 8-10kw
generator, VFX 3648 stacked
> inverters, newer rolls batteries. its been
installed and operating normally
> for 10+ years.
>
> Customer had to
upgrade the house for code, which involved installing GFCI
> outlets and
GFCI breakers.
>
> Since then the GFI outlets trip every time the
generator starts but only
> after 3-30 minutes. They work normally on the
inverters. And if you do a
> bypass/generator direct the GFI outlets don't
trip.
>
> The GFI breakers trip when the generator is about to turn off,
not during
> warm down but say 30 minutes before it will turn off. So
charging current
> is at the lowest. And again they all work normally on
the inverters and all
> the rest of the charge cycle.
>
>
> Voltage is a
bit high, around 254v-259v from the generator but it is the
> whole time
and seems to stable voltage. But if the voltage was the issue
> the outlets
would keep tripping. If it was too high for the breakers, why
> at the end
and not the beginning?
>
> I'm thinking its possibly a control board in
the generator that's not
> working well. Can't keep up with the PF for the
inverters, etc.
>
> Buts its a new issue I've not run across.
>
> Any
ideas?
>
> thanks
>
> jay
>
> peltz power
>
>
>
>
>
_______________________________________________
> List sponsored by Redwood
Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change
listserver email address & settings:
>
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>
There are two list archives for searching. When one doesn't work, try the
>
other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>
List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
>
Check out or update participant bios:
> http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201220/9699817a/attachment.htm>
More information about the RE-Wrenches
mailing list