<pre>One way to troubleshoot this is by elimination. The genset would be a start. The GFCI itself. I have had to switch from the contractor grade GFCI to a quality make in new construction.<br /><br /> Since this is new I would make sure on the AC panel, critical loads like the house pump or fire pumps and refrigerator/ freezer were <strong>not</strong> put on GFCI. I have seen some very bad things happen from this circuit that have nothing to do with ground faults. The same for AFCI or my guaranteed income source from grid-tie inverters.


Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridsolar@sti.net
text 209 813 0060

On Sat, 19 Dec 2020 15:33:36 -0700, jay &lt;jay.peltz@gmail.com&gt; wrote:
&gt; HI All,
&gt; 
&gt; I have a client with a older Kohler 8-10kw generator, VFX 3648 stacked
&gt; inverters, newer rolls batteries. its been installed and operating normally
&gt; for 10+ years.
&gt; 
&gt; Customer had to upgrade the house for code, which involved installing GFCI
&gt; outlets and GFCI breakers.  
&gt; 
&gt; Since then the  GFI outlets trip every time the generator starts but only
&gt; after 3-30 minutes.   They work normally on the inverters. And if you do a
&gt; bypass/generator direct the GFI outlets don&rsquo;t trip.
&gt; 
&gt; The GFI breakers trip when the generator is about to turn off, not during
&gt; warm down but say 30 minutes before it will turn off.  So charging current
&gt; is at the lowest. And again they all work normally on the inverters and all
&gt; the rest of the charge cycle.
&gt; 
&gt; 
&gt; Voltage is a bit high, around 254v-259v from the generator but it is the
&gt; whole time and seems to stable voltage. But if the voltage was the issue
&gt; the outlets would keep tripping.  If it was too high for the breakers, why
&gt; at the end and not the beginning?
&gt; 
&gt; I&rsquo;m thinking its possibly a control board in the generator that&rsquo;s not
&gt; working well.  Can&rsquo;t keep up with the PF for the inverters, etc.  
&gt; 
&gt; Buts its a new issue I&rsquo;ve not run across.
&gt; 
&gt; Any ideas?
&gt; 
&gt; thanks
&gt; 
&gt; jay
&gt; 
&gt; peltz power
&gt; 
&gt; 
&gt; 
&gt; 
&gt; _______________________________________________
&gt; List sponsored by Redwood Alliance
&gt; 
&gt; List Address: RE-wrenches@lists.re-wrenches.org
&gt; 
&gt; Change listserver email address &amp; settings:
&gt; http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
&gt; 
&gt; There are two list archives for searching. When one doesn't work, try the
&gt; other:
&gt; https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
&gt; http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
&gt; 
&gt; List rules &amp; etiquette:
&gt; http://www.re-wrenches.org/etiquette.htm
&gt; 
&gt; Check out or update participant bios:
&gt; http://www.members.re-wrenches.org</pre>