[RE-wrenches] generator tripping GFCI

Jay jay.peltz at gmail.com
Sat Dec 19 19:14:31 EST 2020


Hi Ray

I will have to triple check, but even if it’s yes. 

How does that explain the time differences?  
If it was a neutralground loop,  then why not it tripping everything right away?

That’s why I was thinking it’s related to the control board in the generator?

Jay

> On Dec 19, 2020, at 5:10 PM, Ray <ray at solarray.com> wrote:
> 
> Is it possible that neutral is bonded to ground in the generator?  I've found lots of multi-bonded neutrals over the years, and had it cause all sorts of weirdness.
> 
> Ray Walters
> Remote Solar
> 303 505-8760
> 
>> On 12/19/20 5:33 PM, jay wrote:
>> HI All,
>> 
>> I have a client with a older Kohler 8-10kw generator, VFX 3648 stacked inverters, newer rolls batteries. its been installed and operating normally for 10+ years.
>> 
>> Customer had to upgrade the house for code, which involved installing GFCI outlets and GFCI breakers.
>> 
>> Since then the  GFI outlets trip every time the generator starts but only after 3-30 minutes.   They work normally on the inverters. And if you do a bypass/generator direct the GFI outlets don’t trip.
>> 
>> The GFI breakers trip when the generator is about to turn off, not during warm down but say 30 minutes before it will turn off.  So charging current is at the lowest. And again they all work normally on the inverters and all the rest of the charge cycle.
>> 
>> 
>> Voltage is a bit high, around 254v-259v from the generator but it is the whole time and seems to stable voltage. But if the voltage was the issue the outlets would keep tripping.  If it was too high for the breakers, why at the end and not the beginning?
>> 
>> I’m thinking its possibly a control board in the generator that’s not working well.  Can’t keep up with the PF for the inverters, etc.
>> 
>> Buts its a new issue I’ve not run across.
>> 
>> Any ideas?
>> 
>> thanks
>> 
>> jay
>> 
>> peltz power
>> 
>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches at lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 


More information about the RE-Wrenches mailing list