[RE-wrenches] generator tripping GFCI
Darryl Thayer
darylsolar1 at gmail.com
Sat Dec 19 20:33:43 EST 2020
The way a GFCI operates is by comparing the line current and the neutral
current inside the device. If some of the neutral current is returning
through a ground circuit instead of the neutral the imbalance will trip the
device. The generator neutral and the inverter neutral must have a common
neutral-ground bond and only one!
Your presentation indicates operational differences, multiple bonding
points (two or more) can cause a neutral ground imbalance when load, source
changes occur. The load-source changes can affect the tripping result.
On Sat, Dec 19, 2020 at 5:23 PM jay <jay.peltz at gmail.com> wrote:
> HI All,
>
> I have a client with a older Kohler 8-10kw generator, VFX 3648 stacked
> inverters, newer rolls batteries. its been installed and operating normally
> for 10+ years.
>
> Customer had to upgrade the house for code, which involved installing GFCI
> outlets and GFCI breakers.
>
> Since then the GFI outlets trip every time the generator starts but only
> after 3-30 minutes. They work normally on the inverters. And if you do a
> bypass/generator direct the GFI outlets don’t trip.
>
> The GFI breakers trip when the generator is about to turn off, not during
> warm down but say 30 minutes before it will turn off. So charging current
> is at the lowest. And again they all work normally on the inverters and all
> the rest of the charge cycle.
>
>
> Voltage is a bit high, around 254v-259v from the generator but it is the
> whole time and seems to stable voltage. But if the voltage was the issue
> the outlets would keep tripping. If it was too high for the breakers, why
> at the end and not the beginning?
>
> I’m thinking its possibly a control board in the generator that’s not
> working well. Can’t keep up with the PF for the inverters, etc.
>
> Buts its a new issue I’ve not run across.
>
> Any ideas?
>
> thanks
>
> jay
>
> peltz power
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201219/2cdf1737/attachment.htm>
More information about the RE-Wrenches
mailing list