[RE-wrenches] Sol-Ark Gen Exercise Cycle
Chris Sparadeo
sparadeo.chris at gmail.com
Wed Nov 11 20:20:51 EST 2020
Thanks for the suggestion, Jay.
Yes, the Sol-Ark has a very basic and limited AGS for 2 wire compatible gen
sets. Gen start can be programmed with voltage or SOC, however gen stop is
not a function that can not be readily programmed. Instead, the Sol-Ark is
programmed to charge the battery bank to 90% of the rated Ah capacity of
the battery bank before turning off the generator. You can ultimately
adjust this gen stop parameter to be based on a specific SOC or voltage,
but I believe that doing so requires a call into tech support. The tech I
spoke with updated a setting (having to do with a TOU parameter I believe)
that was not accessible via the system interface. AGS from Schnieder,
Outback and even Magnum are less clunky, but I am hoping that Sol-Ark will
eventually come out with new programming to remediate these minor but
nevertheless, important issues
-Chris
On Wed, Nov 11, 2020 at 3:58 PM Jay <jay.peltz at gmail.com> wrote:
> Hi Chris
>
> I would install a timer. There are many dry contact dc or ac powered with
> a high degree of programmability.
>
> A question about the normal function of the AGS. I’ve talked to a few
> people that have mentioned that the ags has its own fuzzy logic, with
> limited programming. And they have had issues with it not turning on or not
> turning off
>
> What do you say?
>
> Jay
>
> On Nov 11, 2020, at 10:43 AM, Glenn Burt <Glenn.burt at glbcc.com> wrote:
>
>
> I believe the Atkinson GSCM could be used to do this.
>
> -Glenn
> Sent from my 'smart'phone, so please excuse typos and spelling errors.
>
> ------ Original message------
> *From: *Chris Sparadeo
> *Date: *Wed, Nov 11, 2020 11:16 AM
> *To: *RE-wrenches;
> *Cc: *
> *Subject:*[RE-wrenches] Sol-Ark Gen Exercise Cycle
>
> Hi all,
>
> According to Sol-Ark tech support, they do not currently have a
> programmable exercise cycle for
> its two-wire start function. When paired with a generator like a Generac
> Ecogen (exercise cycle is automatically disabled when configured with two
> wire start) this means that the only way to effectively run an exercise
> cycle on your generator would be to do it manually. I am wondering if
> anyone has run into this issue and if there are work arounds? Kind of a
> bummer and my first and only negative experience with Sol-Ark thus far.
>
> Kindly,
>
> Chris Sparadeo
> --
> Chris Sparadeo
>
>
> C_802-369-4458
> H_802-728-3059
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
--
Chris Sparadeo
C_802-369-4458
H_802-728-3059
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201111/5f8613eb/attachment.htm>
More information about the RE-Wrenches
mailing list