[RE-wrenches] unfused disconnect before service disconnect
Jason Szumlanski
jason at floridasolardesigngroup.com
Thu Oct 29 18:03:13 EDT 2020
I'd look at 230.90, 230.91 and 230.94.
I don't think you can argue that the outside disconnect in this scenario is
not the service disconnecting means when it is not service rated. you would
have unprotected service conductors on the line and load side of the
device.
I have just made it a practice to only allow service rated enclosures for
all supply side interconnections. I think it is the most conservative
approach. Not having enough physical space is definitely frustrating.
Jason Szumlanski
On Thu, Oct 29, 2020 at 1:04 PM Dave Tedeyan <dtedeyan at taitem.com> wrote:
> Lloyd,
> I see what you are saying. Although in 250.24, it seems that they are
> expecting this first disconnect to have overcurrent protection and be the
> service disconnecting means. So what if the first disconnect does not have
> overcurrent protection? I am assuming the "service disconnect" is the first
> point of overcurrent protection for the service. What I am thinking of is
> similar to the disconnect allowed on the line side of the meter (230.82
> (3)), although this one is on the load side of the meter.
> Cheers,
> Dave
>
> *Dave Tedeyan, PE*
> Senior Engineer | Taitem Engineering, PC
>
> 110 South Albany Street | Ithaca, NY 14850
> o. *607.277.1118 x121* f. 607.277.2119
> www.taitem.com
> <https://mailtrack.io/trace/link/bf5d06b319267be5a76641988d4606ca49838c57?url=http%3A%2F%2Fwww.taitem.com&userId=1613865&signature=ba98d229bb3fbb14>
>
> Solar • Sustainability • Energy • Design
> Certified B-Corporation since 2013
>
>
> On Thu, Oct 29, 2020 at 12:03 PM Lloyd Hoffstatter <
> lloyd at sunstruckconsulting.com> wrote:
>
>> Dave,
>> Looking at 2014, NEC 250.24(B) FPN and exhibits tends to imply bonding at
>> first means of disconnect. This also minimizes potential ground loops.
>> Best regards,
>> Lloyd Hoffstatter
>> Sunstruck Consulting
>>
>> Get Outlook for iOS
>> <https://mailtrack.io/trace/link/63cc71f967c41c9982b86a7a4271879e3de28a21?url=https%3A%2F%2Faka.ms%2Fo0ukef&userId=1613865&signature=e5b08d5390e82031>
>> ------------------------------
>> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on
>> behalf of Dave Tedeyan <dtedeyan at taitem.com>
>> *Sent:* Thursday, October 29, 2020 9:56:47 AM
>> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
>> *Subject:* [RE-wrenches] unfused disconnect before service disconnect
>>
>> I'm looking to the hive mind here to see if others can weigh in on an
>> issue I am having with an inspector. Grid tied PV system, with a line side
>> tap in an automatic transfer switch. There is an outdoor utility required
>> system disconnect right next to the transfer switch. But there was not
>> enough physical space to get something that was service rated with
>> overcurrent protection. So we installed a QO200TR, which is a tiny switch
>> that looks like a circuit breaker, is rated at 60A, but does not actually
>> have overcurrent protection. Then just inside the basement is the service
>> disconnect with the neutral ground bond, etc. The inspector is telling me
>> to bond the neutral and ground in the outdoor unfused disconnect, and
>> remove it in the disconnect in the basement.
>>
>> I am having trouble finding a code reference. Does anyone know of one
>> showing that the unfused disconnect is not the service point even though it
>> comes first? Or is this not something that is allowed? We are on NEC 2017
>> here in NY..
>> .
>> Thanks!
>> -Dave
>>
>> *Dave Tedeyan, PE*
>> Senior Engineer | Taitem Engineering, PC
>>
>> 110 South Albany Street | Ithaca, NY 14850
>> o. *607.277.1118 x121* f. 607.277.2119
>> www.taitem.com
>> <https://mailtrack.io/trace/link/7cf381d479889e720290cca661851e641ff162a9?url=http%3A%2F%2Fwww.taitem.com&userId=1613865&signature=fd1c5e2a04f92cce>
>>
>> Solar • Sustainability • Energy • Design
>> Certified B-Corporation since 2013
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/72f72b5a7471721d5a72925010cc6ad50ee10bf7?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=6c04ecb8c5e78aa0>
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> <https://mailtrack.io/trace/link/01e9c1cd4631706e2c2db71d97a84624948cd72c?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=45f824ceca8fa868>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/170a02ec45ce79d851a7b34f1969fdd230bdd08f?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=6ba8d46f6d424fbe>
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/543cbac1b8d31cb57aef711389aa854481843816?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=19c3c1188516d3b5>
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/aaa71106c9b58bbd4eff83f281647fdb26894d71?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=ea560c17a8415d20>
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/16b0d881f94ece4ca001d58a04105ffd11e38091?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=1f1998dfa7e96af2>
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> <https://mailtrack.io/trace/link/5f2338ee1028696932be571da556438eb99852ef?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F&userId=1613865&signature=9a19028c338c1bc6>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/1b02e6beff79dc444ee44c5bec21a81808f92eb2?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=69cee8e721a1449e>
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/8dd10a1947409987a5e82eb06bf85fb426aada5d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=95a38e69f548d70a>
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/a54cb438269f50afede6a28b51c5638b74d76fad?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=a048ebbf440f32c5>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201029/27a00a3c/attachment.htm>
More information about the RE-Wrenches
mailing list