Others have pointed this out, but I thought I'd just add a bit of info
based on my experience - the issue is not so much whether you can do a
supply side connection or not, as that is allowed in the code. The issue is
whether you can do wiring in a section of equipment that is only for the
utility. Even though the building owner buys the meter socket, it is
standard that you can't do work in a meter socket section. If we do a
supply side connection, we do it in the section of equipment that is
allowed to be touched by an electrician. In order to allow for a connection
in an actual meter socket section, I would think that the utility would
need to approve it through some sort of official tariff or bulletin
process. Our utility, PG&E, has a document called the Greenbook
<https://www.pge.com/en_US/large-business/services/building-and-renovation/greenbook-manual-online/greenbook-manual-online.page>that
lists their rules. I assume other utilities have the same? Here is an
example of a Green Meter Adapter bulletin that allows for specific
installation of a listed piece of equipment in the meter section:

https://www.pge.com/pge_global/common/pdfs/services/building-and-renovation/greenbook-manual-online/TD-7001B-007.pdf

Good luck out there!

August

On Wed, Oct 28, 2020 at 9:00 AM Kristopher Schmid <solman at legacysolar.com>
wrote:

> Thanks for all the discussion and insight.  I believe the main issue here
> is them being territorial about the meter socket (they did not install it
> and they do not own it).  My follow up question to them was, "I assume that
> you allow a 320 A meter socket feeding two main panels.  Is this
> different?"  Waiting for a response...
>
>
> Shine On!
>
> Kris Schmid
> Legacy Solar, LLC
> 137 West 1st Avenue
> Luck, WI 54853
> www.legacysolar.com
> 715-653-4295
> NABCEP Certified PV Installation Professional
> Licensed Wisconsin Master Electrician
> BSEE
>
>
> On Wed, Oct 28, 2020 at 5:47 AM Christopher Warfel <
> cwarfel at entech-engineering.com> wrote:
>
>> I would think that would be illegal.  They don't have jurisdiction on
>> supply side taps. It's past the meter, and expressly allowed in the NEC.  I
>> would definitely first ask to talk to a higher level person than the one
>> denying it (paper trail important). If that does not work, then the PSC is
>> your best option.  Chris
>> On 10/27/2020 6:27 PM, Kristopher Schmid wrote:
>>
>> Hi All,
>>
>> I have a utility that is hinting that they are going to deny my
>> interconnection application with a supply side connection and require a
>> load side.  Has anyone seen this before?
>>
>> (Proposed interconnection would be with Milbank step lugs in a 200 A
>> socket and a 60 A fused disconnect within 10 feet.)
>>
>> If they refuse it, i am thinking that registering a complaint with the
>> Wisconsin PSC may be appropriate.
>>
>> Kris
>>
>>
>> Shine On!
>>
>> Kris Schmid
>> Legacy Solar, LLC
>> 137 West 1st Avenue
>> Luck, WI 54853
>> www.legacysolar.com
>> 715-653-4295
>> NABCEP Certified PV Installation Professional
>> Licensed Wisconsin Master Electrician
>> BSEE
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:http://www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201028/589479a1/attachment.htm>


More information about the RE-Wrenches mailing list