[RE-wrenches] Supply side denial
drake.chamberlin at redwoodalliance.org
drake.chamberlin at redwoodalliance.org
Tue Oct 27 19:41:42 EDT 2020
AEP Won't let us do a line side tap. We can tap into the line side and
install another service as permitted by the Rule of Six. I have used the
Eaton, 4 space breaker box with 2 spaces for the service disconnect and
2 for the PV connection.
Supposedly you can use a main breaker retainer, according to Eaton tech
support, However, the box doesn't have holes for the screws, but you can
drill a hole in the box and get one screw in. It seems to hold the
breaker firmly.Some inspectors could have an issue with that.
Other manufacturers may have better solutions.
---
On 2020-10-27 18:27, Kristopher Schmid wrote:
> Hi All,
>
> I have a utility that is hinting that they are going to deny my interconnection application with a supply side connection and require a load side. Has anyone seen this before?
>
> (Proposed interconnection would be with Milbank step lugs in a 200 A socket and a 60 A fused disconnect within 10 feet.)
>
> If they refuse it, i am thinking that registering a complaint with the Wisconsin PSC may be appropriate.
>
> Kris
>
> Shine On!
>
> Kris Schmid
> Legacy Solar, LLC
> 137 West 1st Avenue
> Luck, WI 54853
> www.legacysolar.com [1]
> 715-653-4295
> NABCEP Certified PV Installation Professional
> Licensed Wisconsin Master Electrician
> BSEE
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
Links:
------
[1] http://www.legacysolar.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201027/59129480/attachment.htm>
More information about the RE-Wrenches
mailing list