Well Jay, if you call each of those poles "arrays" then you've got a path
around the 2 parallel circuit maximum :)

Note 2020 NEC language has changed a bit, though it's still not crystal
clear:

"PV system dc circuits that exceed 30 volts or 8 amperes shall be provided
with dc ground-fault protection meeting the requirements of 690.41(B)(1)
and (B)(2) to reduce fire hazards.  Solidly grounded PV source circuits
with not more than two modules in parallel and not on or in buildings shall
be permitted without ground-fault protection."

Brian Mehalic
NABCEP Certified Solar PV Installation Professional™ R031508-59
National Electrical Code® CMP-4 Member
(520) 204-6639

Solar Energy International
http://www.solarenergy.org

SEI Professional Services
http://www.seisolarpros.com



On Tue, Oct 27, 2020 at 11:40 AM jay <jay.peltz at gmail.com> wrote:

> HI All,
>
> I’ve got a question about GFDI requirements and do they apply to the
> following.
>
> Here is the project.
>
> 1. water pumping DC direct grundfos SQFLex
>
> 2. no humans anywhere around
>
> 3. no buildings or living structures
>
> 4. would be 3 pole mounts:  each mount as 1 string, so 3 strings.
> 2019 code  690.41 B2 says that 2 modules in parallel without humans
> involved doesn’t need GFDI
>
> 5. system would be solidly grounded.
>
> So what is the requirement for needing GFDI on this project?
>
> thanks
>
> jay
>
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201027/4c47411f/attachment.htm>


More information about the RE-Wrenches mailing list