<div dir="ltr">Well Jay, if you call each of those poles &quot;arrays&quot; then you&#39;ve got a path around the 2 parallel circuit maximum :) <div><br></div><div>





<p class="gmail-p1" style="margin:0px;font-variant-numeric:normal;font-variant-east-asian:normal;font-stretch:normal;line-height:normal;color:rgb(0,0,0)"><font face="arial, sans-serif">Note 2020 NEC language has changed a bit, though it&#39;s still not crystal clear: </font></p><p class="gmail-p1" style="margin:0px;font-variant-numeric:normal;font-variant-east-asian:normal;font-stretch:normal;line-height:normal;color:rgb(0,0,0)"><font face="arial, sans-serif">&quot;PV system dc circuits that exceed 30 volts or 8 amperes shall be provided with dc ground-fault protection meeting the requirements of 690.41(B)(1) and (B)(2) to reduce fire hazards.<span class="gmail-Apple-converted-space" style="">  </span>Solidly grounded PV source circuits with not more than two modules in parallel and not on or in buildings shall be permitted without ground-fault protection.&quot;</font></p><div><div dir="ltr" class="gmail_signature" data-smartmail="gmail_signature"><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><br></div><div>Brian Mehalic <br>NABCEP Certified Solar PV Installation Professional\u2122 R031508-59</div><div>National Electrical CodeŽ CMP-4 Member</div><div>(520) 204-6639<br><div><br></div><div><div><div>Solar Energy International<br><a href="http://www.solarenergy.org" target="_blank">http://www.solarenergy.org</a></div></div></div></div><div><br></div><div>SEI Professional Services</div><div><a href="http://www.seisolarpros.com" target="_blank"><span style="font-size:12.8px">http://www.s</span>eisolarpros.com</a><br></div><div><br></div></div></div></div></div></div></div></div></div></div></div></div><br></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Tue, Oct 27, 2020 at 11:40 AM jay &lt;<a href="mailto:jay.peltz@gmail.com">jay.peltz@gmail.com</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">HI All,<br>
<br>
I\u2019ve got a question about GFDI requirements and do they apply to the following. <br>
<br>
Here is the project.<br>
<br>
1. water pumping DC direct grundfos SQFLex <br>
<br>
2. no humans anywhere around<br>
<br>
3. no buildings or living structures<br>
<br>
4. would be 3 pole mounts:  each mount as 1 string, so 3 strings.<br>
2019 code  690.41 B2 says that 2 modules in parallel without humans involved doesn\u2019t need GFDI<br>
<br>
5. system would be solidly grounded.<br>
<br>
So what is the requirement for needing GFDI on this project?<br>
<br>
thanks<br>
<br>
jay<br>
<br>
<br>
<br>
<br>
<br>
<br>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn&#39;t work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>