I agree, Ray. Shutting down the inverter's ac output and the PV array is 
sufficient to make a battery based system about as safe as possible for 
firefighters. That is probably what was wanted when the code was revised 
to require an outside battery disconnect. Unfortunately, the local AHJ 
may not see it that way. But if the AHJ will agree to it the remote 
inverter shutdown is an easy way to go. I like the way Schneider has 
implemented remote power off in the XW series, once the remote shut off 
is tripped the inverter must be manually reset. I don't believe it is 
done that way in the Outback inverters which leaves open the question: 
can the power come back on if the remote off circuit is compromised. 
Well, it can't if there is a remotely tripped breaker used as a disconnect.

The issue of security for outside disconnects will be a major problem 
that the 2020 code has created. Its not just renewable energy systems in 
that situation. All new utility services have the same requirement. 
Anyone having a beef with their neighbor can shut off their power. Best 
if you wait until they are on vacation...

Kent Osterberg
Blue Mountain Solar


On 10/20/2020 11:24 AM, Ray wrote:
>
> Interesting idea: shutting down the inverter should actually be 
> preferable to a battery disco, since its possible to disconnect the 
> battery and still have an inverter operate array direct if the loads 
> are close to the array output.  I've seen it take several minutes for 
> the inverter to shut off sometimes.
>
> This whole concept needs to be left in the oven longer to get the 
> verbage right.  I believe the idea is to have power off to the 
> distribution circuits in the house, but NEC is having a really hard 
> time just saying that.  Who cares if the battery is still connected to 
> the inverter; there will always be a few feet of battery cable 
> energized, regardless of the remote disconnect scheme.  Seems much 
> easier to shut down the inverter, and then have a clause covering DC 
> distribution for those Luddites still doing that.
>
> Overall, I have severe misgivings about this whole idea.  While it 
> sounds good at first, you must consider that a failure of the remote 
> system, or a wacky neighbor can shut off the entire house including 
> refrigeration and heat.  The customer could come back to rotten food 
> and frozen pipes.  We need to have a more holistic approach that 
> balances fire fighter safety with home owner safety.  Article 445 
> Generators, exempts generators under 15 kW.  It seems something 
> similar for off grid would be appropriate.
>
> How many times has this actually been a problem? or is this possibly 
> just a high tech solution in search of an imagined problem?
>
> Ray Walters
> Remote Solar
> 303 505-8760
> On 10/20/20 9:50 AM, Dave Angelini Offgrid Solar wrote:
>>
>> Thanks Kent,
>>
>> A question, most of the Sierra AHJ's only care, and that is rare, 
>> that there is a remote power off like Outback and Schneider have 
>> already. I understand it is not a battery disco, and even though 
>> there is one in these systems, what is your response please?
>>
>> I mostly dislike power sheds as people need an excuse to go there and 
>> observe. I mostly use a garage or outside house wall to build a bat 
>> room. Appreciate your thoughts. Insurance issues are not as important 
>> these days as many of us no longer can get itCry
>>
>>   
>> *Dave Angelini Offgrid Solar "we go where powerlines don't" 
>> http://members.sti.net/offgridsolar/ e-mail offgridsolar at sti.net 
>> <mailto:offgridsolar at sti.net> text 209 813 0060*
>>
>> On Mon, 19 Oct 2020 22:33:03 -0700, Kent Osterberg 
>> <kent at coveoregon.com> wrote:
>>
>>> Ray,
>>>
>>> Per NEC 480 batteries below 48 volts didn't need a readily 
>>> accessible disconnect within site of the batteries. That's unchanged 
>>> in the 2020 Code, you don't have to have a readily accessible 
>>> disconnect within site of the batteries. That's a good thing 
>>> considering the environment near lead acid batteries. A disconnect 
>>> switch still isn't required in the 48-volt battery room.
>>>
>>> Yes, if you put a 48-volt battery in a one or two-family dwelling, 
>>> an outside (remote) emergency disconnect is required. That is going 
>>> to be a pain that may add hundreds of dollars to the cost of small 
>>> off-grid systems. You might get away with a mushroom switch and a 
>>> 24-volt tap on the batteries to activate a remote trip breaker. But 
>>> considering that it is a fire-safety related circuit it is probably 
>>> best to spend the money for the bird box.
>>>
>>> At the very least 480.7(B) should make off-grid folks think about 
>>> using a power shed. The power shed is not a dwelling so 2020 NEC 
>>> 480.7(B) doesn't apply.
>>>
>>> Kent Osterberg
>>> Blue Mountain Solar
>>>
>>>
>>> On 10/19/2020 8:34 PM, Ray wrote:
>>>>
>>>> I've used Blue Planet, so I guess I have used an actual UL listed 
>>>> ESS, even though they don't include the charge controller or 
>>>> inverter.  I knew they were UL, but I double checked and it is the 
>>>> UL 9540 standard mentioned in 706. So in this case, we could ignore 
>>>> 480, but are held to 706.  Regardless of 480 or 706, both are 
>>>> possibly requiring the outside remote disconnect.  Besides 
>>>> Midnite's remote trip breakers, and the dreaded Bird House, what 
>>>> other options are there to meet this new requirement?   Can the 
>>>> Blue Planet be tripped remotely?
>>>>
>>>> and still my initial question:
>>>>
>>>> Under 480.7, are batteries below 60v still required to have the 
>>>> remote disconnect?  They are exempted from having a disconnect at 
>>>> all in 480.7(A)......quite confusing.
>>>>
>>>> Ray Walters
>>>> Remote Solar
>>>> 303 505-8760
>>>> On 10/19/20 7:06 PM, Jerry Shafer wrote:
>>>>> Wrenches
>>>>> Blue planet are fire and UL listed systems both on there 48 Volt 
>>>>> and the LX flavors
>>>>> Jerry
>>>>>
>>>>> On Mon, Oct 19, 2020, 5:51 PM Ray <ray at solarray.com 
>>>>> <mailto:ray at solarray.com>> wrote:
>>>>>
>>>>>     The notes in the NEC 2020 Handbook for article 706 clearly
>>>>>     state that 706 only covers ESS which is an assembly of
>>>>>     components, and that the total assembly must be listed under
>>>>>     UL 9540.
>>>>>
>>>>>     Further it states: "/A group of separate components that
>>>>>     includes storage batteries, that is provided with support
>>>>>     systems (racks), charge controllers, and inverters, and that
>>>>>     does NOT have an overall listing as an ESS is a storage
>>>>>     battery system and as such is subject to the requirements of
>>>>>     article 480"/
>>>>>
>>>>>     and just in case someone says the notes don't matter, 706.5
>>>>>     says: "/Energy Storage systems shall be listed"/.
>>>>>
>>>>>     So, since I have never used an actual listed ESS, I'm back to
>>>>>     480. Specifically, 480.7 (A) says we need a disconnect for
>>>>>     batteries over 60 vdc (48v should be exempt) and then 480.7(B)
>>>>>     says houses need to have an outside disconnect for the
>>>>>     batteries labeled "Emergency Disconnect".
>>>>>
>>>>>     So here's the real question:   Does 480.7(A) exempt us from
>>>>>     480.7(B)?
>>>>>
>>>>>     Ray Walters
>>>>>     Remote Solar
>>>>>     303 505-8760
>>>>>
>>>>>     On 3/9/19 8:08 PM, Brian Mehalic wrote:
>>>>>>     Hi Glenn, I don't completely agree with your interpretation
>>>>>>     of ESS systems and the application of Article 706.  Yes, an
>>>>>>     ESS /could/ provide 120/240 VAC (e.g. the Powerwall), but the
>>>>>>     figures in Article 690 show three different configurations
>>>>>>     where the output of the ESS is not AC, and where the ESS
>>>>>>     disconnect comes before any power electronics (like a
>>>>>>     multimode inverter, as shown in the AC and DC coupled
>>>>>>     systems) or loads (as shown in the stand-alone system). Are
>>>>>>     those ESS connected to other systems which utilize stored
>>>>>>     energy to provide AC power? Yes, but the key is "connected to
>>>>>>     other systems" - in many cases the ESS only provides DC.  In
>>>>>>     fact the definition of ESS clearly states this - it
>>>>>>     /can/ have AC or DC output, and it /may/ include power
>>>>>>     electronics (but may not).
>>>>>>     My understanding is that the 60 volt limit (which is
>>>>>>     obviously problematic in a world where 48 VDC batteries and
>>>>>>     ESS are very common) was inserted in order to exempt other
>>>>>>     devices that store energy (such as UPS, or battery backup in
>>>>>>     fire alarms/exit signage/etc.) from the 706 requirements.
>>>>>>     Cheers,
>>>>>>     Brian Mehalic
>>>>>>     NABCEP Certified Solar PV Installation Professional™ R031508-59
>>>>>>     National Electrical Code® CMP-4 Member
>>>>>>     (520) 204-6639
>>>>>>     Solar Energy International
>>>>>>     http://www.solarenergy.org
>>>>>>     SEI Professional Services
>>>>>>     http://www.seisolarpros.com <http://www.seisolarpros.com>
>>>>>>
>>>>>>     On Sat, Mar 9, 2019 at 4:07 PM Glenn Burt
>>>>>>     <glenn.burt at glbcc.com <mailto:glenn.burt at glbcc.com>> wrote:
>>>>>>
>>>>>>         Hi Ray,
>>>>>>
>>>>>>         This is a conversation I have had some time ago with a
>>>>>>         number of my fellow inspectors and code experts. When the
>>>>>>         2017 NEC came out, I agreed with Mike Holt and Bill
>>>>>>         Brooks' assessment that the new article was poorly
>>>>>>         written and did not apply to most systems being installed
>>>>>>         today. After much discussion through my Cadmus network of
>>>>>>         authorities, it emerged that indeed 706 apples to the
>>>>>>         typical residential systems.
>>>>>>         So Energy Storage Systems (ESS) are the point of article
>>>>>>         706, and I believe that the key point is that the SYSTEM
>>>>>>         is generating AC voltage of 120VAC or 240VAC, making the
>>>>>>         system fall under article 706.
>>>>>>
>>>>>>         Batteries themselves are minimally covered by NEC 480,
>>>>>>         NFPA 1, and the IFC as applicable locally.
>>>>>>         So, the bottom line is that the new article does cover
>>>>>>         the work we do when systems provide or interface with
>>>>>>         120VAC or above (making the system operation exceeding
>>>>>>         the 60V AC trigger).
>>>>>>
>>>>>>         My initial problem was believing that the article applied
>>>>>>         to a component (the battery bank), and not the system
>>>>>>         (all components taken together as a generator/storage
>>>>>>         system). It is an easy misunderstanding to make.
>>>>>>
>>>>>>         Hope this helps!
>>>>>>
>>>>>>         -Glenn Burt
>>>>>>
>>>>>>         -----Original Message-----
>>>>>>         From: RE-wrenches
>>>>>>         <re-wrenches-bounces at lists.re-wrenches.org
>>>>>>         <mailto:re-wrenches-bounces at lists.re-wrenches.org>> On
>>>>>>         Behalf Of Ray
>>>>>>         Sent: Saturday, March 09, 2019 12:41 PM
>>>>>>         To: RE-wrenches <re-wrenches at lists.re-wrenches.org
>>>>>>         <mailto:re-wrenches at lists.re-wrenches.org>>
>>>>>>         Cc: Bill Brooks <billb at energy808.com
>>>>>>         <mailto:billb at energy808.com>>; Bill Brooks
>>>>>>         <billbrooks7 at yahoo.com <mailto:billbrooks7 at yahoo.com>>
>>>>>>         Subject: [RE-wrenches] NEC for Batteries < 60v ??
>>>>>>
>>>>>>         Hi Everyone;
>>>>>>
>>>>>>         I'm updating all my verbage on plansets, and I just
>>>>>>         realized that the newly created article 706 covering
>>>>>>         Energy Storage Systems is only for Over 60 VDC (706.1) 
>>>>>>         Also article 480 for batteries only requires
>>>>>>         disconnecting means over 60 VDC ?! (480.7).   I'm not
>>>>>>         about to not have a disconnect, so now that NEC pulled
>>>>>>         battery systems out of 690,  where do we go for guidance
>>>>>>         on normal battery systems: 12, 24, 48 VDC?
>>>>>>
>>>>>>         Overall, I welcome most of the changes in NEC 2017, like
>>>>>>         separating off grid systems into articles 706, and 710,
>>>>>>         but it seems us off grid installers need some more
>>>>>>         clarification.
>>>>>>
>>>>>>         Thanks,
>>>>>>
>>>>>>         --
>>>>>>         Ray Walters
>>>>>>         Remote Solar
>>>>>>         303 505-8760
>>>>>>
>>>>>>         _______________________________________________
>>>>>>         List sponsored by Redwood Alliance
>>>>>>
>>>>>>         List Address: RE-wrenches at lists.re-wrenches.org
>>>>>>         <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>>
>>>>>>         Change listserver email address & settings:
>>>>>>         http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>
>>>>>>         List-Archive:
>>>>>>         http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>>>
>>>>>>         List rules & etiquette:
>>>>>>         www.re-wrenches.org/etiquette.htm
>>>>>>         <http://www.re-wrenches.org/etiquette.htm>
>>>>>>
>>>>>>         Check out or update participant bios:
>>>>>>         www.members.re-wrenches.org
>>>>>>         <http://www.members.re-wrenches.org>
>>>>>>
>>>>>>
>>>>>>         _______________________________________________
>>>>>>         List sponsored by Redwood Alliance
>>>>>>
>>>>>>         List Address: RE-wrenches at lists.re-wrenches.org
>>>>>>         <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>>
>>>>>>         Change listserver email address & settings:
>>>>>>         http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>
>>>>>>         List-Archive:
>>>>>>         http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>>>
>>>>>>         List rules & etiquette:
>>>>>>         www.re-wrenches.org/etiquette.htm
>>>>>>         <http://www.re-wrenches.org/etiquette.htm>
>>>>>>
>>>>>>         Check out or update participant bios:
>>>>>>         www.members.re-wrenches.org
>>>>>>         <http://www.members.re-wrenches.org>
>>>>>>
>>>>>>
>>>>>>     _______________________________________________
>>>>>>     List sponsored by Redwood Alliance
>>>>>>
>>>>>>     List Address:RE-wrenches at lists.re-wrenches.org  <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>>
>>>>>>     Change listserver email address & settings:
>>>>>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>
>>>>>>     List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>>>
>>>>>>     List rules & etiquette:
>>>>>>     www.re-wrenches.org/etiquette.htm  <http://www.re-wrenches.org/etiquette.htm>
>>>>>>
>>>>>>     Check out or update participant bios:
>>>>>>     www.members.re-wrenches.org  <http://www.members.re-wrenches.org>
>>>>>>
>>>>>     _______________________________________________
>>>>>     List sponsored by Redwood Alliance
>>>>>
>>>>>     List Address: RE-wrenches at lists.re-wrenches.org
>>>>>     <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>
>>>>>     Change listserver email address & settings:
>>>>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>>     There are two list archives for searching. When one doesn't
>>>>>     work, try the other:
>>>>>     https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>>     http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>
>>>>>     List rules & etiquette:
>>>>>     http://www.re-wrenches.org/etiquette.htm
>>>>>
>>>>>     Check out or update participant bios:
>>>>>     http://www.members.re-wrenches.org
>>>>>
>>>>>
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>>
>>>>> List Address:RE-wrenches at lists.re-wrenches.org
>>>>>
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>> There are two list archives for searching. When one doesn't work, try the other:
>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org
>>>>>
>>>>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> List Address:RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> There are two list archives for searching. When one doesn't work, try the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address:RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201020/4057bffc/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: smiley-cry.gif
Type: image/gif
Size: 329 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20201020/4057bffc/attachment.gif>


More information about the RE-Wrenches mailing list