[RE-wrenches] dual rated 600/1000v cable for HV battery application
Ray
ray at solarray.com
Tue Aug 4 14:49:19 EDT 2020
I've used it a few times for battery and inverter cables and it works
just fine. It just has a thicker jacket so when you heat shrink it at
the lugs, it looks funny. Not a serious problem, just get a higher
ratio heat shrink like 3 to 1, and it should be fine.
Ray Walters
Remote Solar
303 505-8760
On 8/4/20 12:32 PM, Kirk Herander wrote:
> Thanks Ray,
> I am going to use the 2kva DLO cable. It is dual rated as RHW-2, which
> is what inverter OEM recommends. AWC warehouse is also close by in PA.
> also.
>>
>> On 8/1/2020 8:16:16 PM, Ray <ray at solarray.com> wrote:
>>
>> I would look at Diesel Locomotive Cable DLO, which is usually dual
>> rated RHH/RHW-2 for us non locomotive folks. 2000 v rated. Its
>> pretty easy to work with, flexible, but has a 2nd inner liner that
>> gives it the higher volt rating. Its also usually tinned conductors
>> too.
>>
>> https://www.awcwire.com/productspec.aspx?id=dlo
>>
>> Ray Walters
>> Remote Solar
>> 303 505-8760
>> On 8/1/20 7:09 AM, Kirk Herander wrote:
>>> I need to spec battery cable for a nominal 850 vdc LFP bank. Several
>>> brands of power cable list their rating at a dual 600/1000v. it is
>>> my understanding that to be listed in this manner, the cable must
>>> pass a test apply of over 600v for a short period without
>>> breakdown. But under normal operation IMO, the voltage is not to
>>> exceed 600v. And this test is done with AC voltage, not DC.
>>>
>>> "*UL 1277: Power and Control Tray Cable*
>>>
>>> UL 1277, the standard for electrical power and control tray cable,
>>> was recently updated, allowing manufacturers with UL approved tray
>>> cable to market their product as 600V/1kV rated. To be dual rated,
>>> products must use a recognized 1kV rated conductor and pass a higher
>>> voltage AC Hipot test on the completed cable. This test requires
>>> each insulated conductor in finished cable to withstand a specified
>>> voltage range for one minute without breakdown. If a product passes
>>> the AC Hipot test, it is suitable for 1kV use."
>>>
>>>
>>> Am I getting this right? And If so, one should not use this
>>> 600/1000v wire if normal operating voltage is above 600v as is my
>>> case? Proper rating should be dual 1000/2000v like PV wire?
>>>
>>> What do you experienced high voltage battery gurus use in my
>>> application? Thanks.
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address:RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200804/9827bb62/attachment.htm>
More information about the RE-Wrenches
mailing list