    <p>I've used it a few times for battery and inverter cables and it
      works just fine.  It just has a thicker jacket so when you heat
      shrink it at the lugs, it looks funny.  Not a serious problem,
      just get a higher ratio heat shrink like 3 to 1, and it should be
      fine. <br>
    </p>
    <pre class="moz-signature" cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
    <div class="moz-cite-prefix">On 8/4/20 12:32 PM, Kirk Herander
      wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:Mailbird-7cdf471f-def6-4368-a84e-84f193f18a6c@icloud.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div id="__MailbirdStyleContent" style="font-size:
        12pt;font-family: Arial;color: #000000"> Thanks Ray,
        <div>I am going to use the 2kva DLO cable. It is dual rated as
          RHW-2, which is what inverter OEM recommends. AWC warehouse is
          also close by in PA. also.</div>
        <blockquote class="history_container" type="cite"
          style="border-left-style:solid;border-width:1px;
          margin-top:20px; margin-left:0px;padding-left:10px;">
          <p style="color: #AAAAAA; margin-top: 10px;">On 8/1/2020
            8:16:16 PM, Ray <a class="moz-txt-link-rfc2396E" href="mailto:ray@solarray.com">&lt;ray@solarray.com&gt;</a> wrote:</p>
          <div style="font-family:Arial,Helvetica,sans-serif">
            <p>I would look at Diesel Locomotive Cable  DLO, which is
              usually dual rated RHH/RHW-2 for us non locomotive folks. 
              2000 v rated.  Its pretty easy to work with, flexible, but
              has a 2nd inner liner that gives it the higher volt
              rating.  Its also usually tinned conductors too.  <br>
            </p>
            <p><a href="https://www.awcwire.com/productspec.aspx?id=dlo"
                moz-do-not-send="true">https://www.awcwire.com/productspec.aspx?id=dlo</a></p>
            <pre class="moz-signature" cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
            <div class="moz-cite-prefix">On 8/1/20 7:09 AM, Kirk
              Herander wrote:<br>
            </div>
            <blockquote type="cite"
              cite="mid:Mailbird-03b102ef-a1ab-4ac4-8691-60e160fbc8f2@icloud.com">
              <div id="__MailbirdStyleContent" style="font-size:
                12pt;font-family: Arial;color: #000000">I need to spec
                battery cable for a nominal 850 vdc LFP bank. Several
                brands of power cable list their rating at a dual
                600/1000v. it is my understanding that to be listed in
                this manner, the cable must pass a test apply of over
                600v for a short period  without breakdown. But under
                normal operation IMO, the voltage is not to exceed 600v.
                And this test is done with AC voltage, not DC.
                <div><span style="font-size: 12pt;color: rgb(51, 51,
                    51);font-family: oswald, sans-serif"><br>
                  </span></div>
                <div><span style="font-size: 12pt;color: rgb(51, 51,
                    51);font-family: oswald, sans-serif">"<b>UL 1277:
                      Power and Control Tray Cable</b></span><br>
                </div>
                <div>
                  <p style="box-sizing: border-box; margin-bottom: 8px;
                    margin-top: 0px; padding-top: 0px; padding-bottom:
                    0px; color: rgb(51, 51, 51); font-family: lato,
                    sans-serif; line-height: 22px; text-size-adjust:
                    none;">UL 1277, the standard for electrical power
                    and control tray cable, was recently updated,
                    allowing manufacturers with UL approved tray cable
                    to market their product as 600V/1kV rated. To be
                    dual rated, products must use a recognized 1kV rated
                    conductor and pass a higher voltage AC Hipot test on
                    the completed cable. This test requires each
                    insulated conductor in finished cable to withstand a
                    specified voltage range for one minute without
                    breakdown. If a product passes the AC Hipot test, it
                    is suitable for 1kV use."</p>
                  <div><br>
                  </div>
                  <div>Am I getting this right? And If so, one should
                    not use this 600/1000v wire if normal operating
                    voltage is above 600v as is my case? Proper rating
                    should be dual 1000/2000v like PV wire?</div>
                  <div><br>
                  </div>
                  <div>What do you experienced high voltage battery
                    gurus use in my application? Thanks.</div>
                </div>
              </div>
              <br>
              <fieldset class="mimeAttachmentHeader"></fieldset>
              <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" moz-do-not-send="true">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm" moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org" moz-do-not-send="true">www.members.re-wrenches.org</a>

</pre>
            </blockquote>
          </div>
        </blockquote>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>