[RE-wrenches] dual rated 600/1000v cable for HV battery application
Tump
tump at swnl.net
Mon Aug 3 09:47:38 EDT 2020
My contact at Cobra wire & cable is quite sharp. 215-674-8773 ext. 5000, ltashjian at cobrawire.com <mailto:ltashjian at cobrawire.com> she has been CCed here.
> On Aug 1, 2020, at 8:16 PM, Ray <ray at solarray.com> wrote:
>
> I would look at Diesel Locomotive Cable DLO, which is usually dual rated RHH/RHW-2 for us non locomotive folks. 2000 v rated. Its pretty easy to work with, flexible, but has a 2nd inner liner that gives it the higher volt rating. Its also usually tinned conductors too.
> https://www.awcwire.com/productspec.aspx?id=dlo <https://www.awcwire.com/productspec.aspx?id=dlo>
> Ray Walters
> Remote Solar
> 303 505-8760
> On 8/1/20 7:09 AM, Kirk Herander wrote:
>> I need to spec battery cable for a nominal 850 vdc LFP bank. Several brands of power cable list their rating at a dual 600/1000v. it is my understanding that to be listed in this manner, the cable must pass a test apply of over 600v for a short period without breakdown. But under normal operation IMO, the voltage is not to exceed 600v. And this test is done with AC voltage, not DC.
>>
>> "UL 1277: Power and Control Tray Cable
>> UL 1277, the standard for electrical power and control tray cable, was recently updated, allowing manufacturers with UL approved tray cable to market their product as 600V/1kV rated. To be dual rated, products must use a recognized 1kV rated conductor and pass a higher voltage AC Hipot test on the completed cable. This test requires each insulated conductor in finished cable to withstand a specified voltage range for one minute without breakdown. If a product passes the AC Hipot test, it is suitable for 1kV use."
>>
>>
>> Am I getting this right? And If so, one should not use this 600/1000v wire if normal operating voltage is above 600v as is my case? Proper rating should be dual 1000/2000v like PV wire?
>>
>> What do you experienced high voltage battery gurus use in my application? Thanks.
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>
>> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> Tump at swnl.net <blocked::mailto:Tump at swnl.net%22%20%5Co%20%22blocked::mailto:Tump at swnl.net> www.SWNL.net <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
> Solarwinds Northernlights
> Serving Mid Coast Maine & Northern California
> 207-832-7574 Cl. 610-517-8401
> Blair "TUMP" May
> ******** MAINE'S CHARTER ********
> NABCEP "Certified PV Installer"
>
> ******** MAINE'S CHARTER ********
> Trace Xantrex "Certified" Dealer / Installer"
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200803/b5eb717c/attachment.htm>
More information about the RE-Wrenches
mailing list