I would look at Diesel Locomotive Cable  DLO, which is usually dual 
rated RHH/RHW-2 for us non locomotive folks.  2000 v rated. Its pretty 
easy to work with, flexible, but has a 2nd inner liner that gives it the 
higher volt rating.  Its also usually tinned conductors too.

https://www.awcwire.com/productspec.aspx?id=dlo

Ray Walters
Remote Solar
303 505-8760

On 8/1/20 7:09 AM, Kirk Herander wrote:
> I need to spec battery cable for a nominal 850 vdc LFP bank. Several 
> brands of power cable list their rating at a dual 600/1000v. it is my 
> understanding that to be listed in this manner, the cable must pass a 
> test apply of over 600v for a short period  without breakdown. But 
> under normal operation IMO, the voltage is not to exceed 600v. And 
> this test is done with AC voltage, not DC.
>
> "*UL 1277: Power and Control Tray Cable*
>
> UL 1277, the standard for electrical power and control tray cable, was 
> recently updated, allowing manufacturers with UL approved tray cable 
> to market their product as 600V/1kV rated. To be dual rated, products 
> must use a recognized 1kV rated conductor and pass a higher voltage AC 
> Hipot test on the completed cable. This test requires each insulated 
> conductor in finished cable to withstand a specified voltage range for 
> one minute without breakdown. If a product passes the AC Hipot test, 
> it is suitable for 1kV use."
>
>
> Am I getting this right? And If so, one should not use this 600/1000v 
> wire if normal operating voltage is above 600v as is my case? Proper 
> rating should be dual 1000/2000v like PV wire?
>
> What do you experienced high voltage battery gurus use in my 
> application? Thanks.
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200801/177cb5bc/attachment.htm>


More information about the RE-Wrenches mailing list