That is an excellent observation.  I instinctively surmised what was
intended, but I missed that the drawing violates schematic norms in a big
way.  (Or does the drawing indicate that the Powerwall2 is so awesome you
can sell generator power to the grid with the Powerwall2 not even
connected?)



William



*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *Jason Szumlanski
*Sent:* Tuesday, July 21, 2020 1:59 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Tesla Powerwall 2.0 - Experience?



Whoever drew that up made it look like the generator is the common pole. I
know what they were getting at, but it's a pretty poor way of depicting it.







On Mon, Jul 20, 2020 at 6:15 PM larry at starlightsolar.com <
larry at starlightsolar.com> wrote:

This, from a Nov 03, 2017 Powerwall 2 document, makes sense. Generator
input in place of utility syncs with PV inverters and Powerwall inverter.


Thank you,

Larry Crutcher
Starlight Solar Power Systems





On Jul 20, 2020, at 1:25 PM, August Goers <august at luminalt.com> wrote:

Tesla released new offgrid design and installation instructions April of
this year. As a Powerwall dealer, we're under NDA not to share
the document, but the Powerwall will now charge from the generator when it
hits a certain SOC threshold if the PV is not running. I'm not sure about
that caveat of not allowing the generator to run while the PV is running.
It seems like there are plenty of times where there is low solar production
and you want to fire up the generator to top off the batteries. They also
have a low state of charge mode when SOC reaches 10%, that the Powerwall
will turn on during the day for short periods of time just to test to see
if the PV system will couple up to charge the battery. This AC-coupling
method of reviving the battery may or not work depending on loads and PV
sizing / production levels.

One limitation to the NMC battery technology is that it doesn't work well
particularly in the cold, so offrige Powerwall batteries should
be installed in the heated envelope of the home.

August


On Mon, Jul 20, 2020 at 10:09 AM Jason Szumlanski <
jason at floridasolardesigngroup.com> wrote:
The Powerwall 2 is now supported by Tesla in an off-grid configuration from
what I heard. It is AC coupled. It cannot interact with generators
whatsoever. You can't charge the battery with a generator and you can't AC
couple a generator to it. If you want a generator, you put a transfer
switch on the load side of the gateway device. If the battery dies, the
generator starts. The generator powers loads, but does not recharge the
battery because it becomes isolated via the transfer switch. The big
downside I see with that is there would be a loss of power to the loads
until the generator fires up. I don't see a way around that.

I'm not a Tesla certified installer, but I have seen some of these
batteries out in the wild and that's just the way it is - it's an
integrated unit. I'd call it an "AC Battery," kind of like an AC PV Module.
To answer another point in this thread, if the battery reaches its LBCO
it can only recharge with PV in an off-grid scenario. It reserves battery
capacity to turn on occasionally to see if there is PV input. At least
that's how I understand it to work. I don't know what would happen if the
battery actually reached 0%. Seems risky. I'm not sure how you would "jump
start" it. Publicly available details seem scant on this, but there are a
few system owners talking about it if you dig deep on the Interwebs.

It will be interesting to see what Enphase comes up with. There are
generator inputs on their Ensemble system, but no software support for this
yet. The concept is very similar to Tesla in that there is a gateway
device, essentially a transfer switch with battery controls inside. The
Gateway acts as the AC point of coupling for everything to tie in together.

I'm not sure why you couldn't use a generator to charge the Powerwall
battery the same way you would charge with the grid. However, you would
need a way to disable PV AC coupling when the generator is running. I can
see how Enphase would be able to do this pretty easily. But Tesla is clear
in that they do not allow a generator to interact with the Powerwall in any
way.

Jason Szumlanski





On Sun, Jul 19, 2020 at 11:43 AM Hilton Dier III <hiltondier at gmail.com>
wrote:
Greetings, Wrenches,

I have an off-grid client who has been reading the buzz about the Tesla
Powerwall 2.0. I have been reading the data sheets and manual for it and it
appears to be AC coupled only. There was talk of a DC input version, but
apparently that fell by the wayside. I try to be agnostic about technology,
and I'd be willing to subcontract a Tesla-approved installer if, in fact,
this was the best solution.

Does anybody have experience using the Powerwall 2.0 in an off grid PV
system? Is it AC coupled only? Can it take generator power
without barfing? What is the lead time on these?

Many Thanks,

Hilton

-- 

Hilton Dier III

Missisquoi River Hydro

Renewable Energy Design


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
<https://mailtrack.io/trace/link/f6ea4b30723a9bc5b29d047f6da2806b0296e922?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=b5c46602d9fb0d59>

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
<https://mailtrack.io/trace/link/8b291ee2dec6e8234cf52ede4191455626474080?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=ad1274bbc70810a0>

List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<https://mailtrack.io/trace/link/836add2fd0522d76b8f2bbe2c2f6f9e28c187658?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=acb9de097dc846a7>

Check out or update participant bios:
www.members.re-wrenches.org
<https://mailtrack.io/trace/link/ccc22d879d66d5c04a98a5c61d2625cc9d88ad5a?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=6e54e76130737629>


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
<https://mailtrack.io/trace/link/c3567926e34d0ddc91e187d38e0390893398cf9a?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=b1afac8bc6ba3ed5>

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
<https://mailtrack.io/trace/link/ced87960a6603faabfa804649b2f1c5c4b5b3b47?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=5f935d7ea9bf964c>

List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<https://mailtrack.io/trace/link/433222a0ac85c07cdc8ba1828518cde18ab5adf9?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=4c905b2fc1e823ba>

Check out or update participant bios:
www.members.re-wrenches.org
<https://mailtrack.io/trace/link/76871e1902dfa610f585b1b8dc8d37803abea73b?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=0c1c1a6bc7f41415>

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
<https://mailtrack.io/trace/link/27eaa17f79779836c455bbff32e18fd018424574?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=134646e4a1c18f11>

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
<https://mailtrack.io/trace/link/9887f4d348a66e425d01a57112af65ed37c6c499?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=c4b5dcfd78cf3e96>

List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<https://mailtrack.io/trace/link/07092b59323827b81acf7a298b5f0a30c7d35ab9?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=1cc273a297a298b4>

Check out or update participant bios:
www.members.re-wrenches.org
<https://mailtrack.io/trace/link/e2b1398da3d843e9f51f06dce9bf4f1b50c0ed2f?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=cbe1cd1484640e62>

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
<https://mailtrack.io/trace/link/2bf40c8b8866f16c2ded3a68a6f703cd0b0c54c0?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=8b6b3c444e491b13>

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
<https://mailtrack.io/trace/link/ee5fe555334e1c91d60628c67cce819823f9657a?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=e20ae3b19e9fcdee>

List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<https://mailtrack.io/trace/link/62a02cc889afa40d0ded59e2b4be33d0bf30d776?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=b60a2a8229423741>

Check out or update participant bios:
www.members.re-wrenches.org
<https://mailtrack.io/trace/link/dc7807d233f3d021a21cfed7bd175235e3d866a0?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=1f083b0951b87587>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200721/61960c88/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 23471 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200721/61960c88/attachment.png>


More information about the RE-Wrenches mailing list