[RE-wrenches] Tesla Powerwall 2.0 - Experience?
Jason Szumlanski
jason at floridasolardesigngroup.com
Tue Jul 21 16:58:45 EDT 2020
Whoever drew that up made it look like the generator is the common pole. I
know what they were getting at, but it's a pretty poor way of depicting it.
On Mon, Jul 20, 2020 at 6:15 PM larry at starlightsolar.com <
larry at starlightsolar.com> wrote:
> This, from a Nov 03, 2017 Powerwall 2 document, makes sense. Generator
> input in place of utility syncs with PV inverters and Powerwall inverter.
>
> Thank you,
>
> Larry Crutcher
> Starlight Solar Power Systems
>
>
>
>
>
>
> On Jul 20, 2020, at 1:25 PM, August Goers <august at luminalt.com> wrote:
>
> Tesla released new offgrid design and installation instructions April of
> this year. As a Powerwall dealer, we're under NDA not to share
> the document, but the Powerwall will now charge from the generator when it
> hits a certain SOC threshold if the PV is not running. I'm not sure about
> that caveat of not allowing the generator to run while the PV is running.
> It seems like there are plenty of times where there is low solar production
> and you want to fire up the generator to top off the batteries. They also
> have a low state of charge mode when SOC reaches 10%, that the Powerwall
> will turn on during the day for short periods of time just to test to see
> if the PV system will couple up to charge the battery. This AC-coupling
> method of reviving the battery may or not work depending on loads and PV
> sizing / production levels.
>
> One limitation to the NMC battery technology is that it doesn't work well
> particularly in the cold, so offrige Powerwall batteries should
> be installed in the heated envelope of the home.
>
> August
>
>
> On Mon, Jul 20, 2020 at 10:09 AM Jason Szumlanski <
> jason at floridasolardesigngroup.com> wrote:
> The Powerwall 2 is now supported by Tesla in an off-grid configuration
> from what I heard. It is AC coupled. It cannot interact with generators
> whatsoever. You can't charge the battery with a generator and you can't AC
> couple a generator to it. If you want a generator, you put a transfer
> switch on the load side of the gateway device. If the battery dies, the
> generator starts. The generator powers loads, but does not recharge the
> battery because it becomes isolated via the transfer switch. The big
> downside I see with that is there would be a loss of power to the loads
> until the generator fires up. I don't see a way around that.
>
> I'm not a Tesla certified installer, but I have seen some of these
> batteries out in the wild and that's just the way it is - it's an
> integrated unit. I'd call it an "AC Battery," kind of like an AC PV Module.
> To answer another point in this thread, if the battery reaches its LBCO
> it can only recharge with PV in an off-grid scenario. It reserves battery
> capacity to turn on occasionally to see if there is PV input. At least
> that's how I understand it to work. I don't know what would happen if the
> battery actually reached 0%. Seems risky. I'm not sure how you would "jump
> start" it. Publicly available details seem scant on this, but there are a
> few system owners talking about it if you dig deep on the Interwebs.
>
> It will be interesting to see what Enphase comes up with. There are
> generator inputs on their Ensemble system, but no software support for this
> yet. The concept is very similar to Tesla in that there is a gateway
> device, essentially a transfer switch with battery controls inside. The
> Gateway acts as the AC point of coupling for everything to tie in together.
>
> I'm not sure why you couldn't use a generator to charge the Powerwall
> battery the same way you would charge with the grid. However, you would
> need a way to disable PV AC coupling when the generator is running. I can
> see how Enphase would be able to do this pretty easily. But Tesla is clear
> in that they do not allow a generator to interact with the Powerwall in any
> way.
>
> Jason Szumlanski
>
>
>
>
>
> On Sun, Jul 19, 2020 at 11:43 AM Hilton Dier III <hiltondier at gmail.com>
> wrote:
> Greetings, Wrenches,
>
> I have an off-grid client who has been reading the buzz about the Tesla
> Powerwall 2.0. I have been reading the data sheets and manual for it and it
> appears to be AC coupled only. There was talk of a DC input version, but
> apparently that fell by the wayside. I try to be agnostic about technology,
> and I'd be willing to subcontract a Tesla-approved installer if, in fact,
> this was the best solution.
>
> Does anybody have experience using the Powerwall 2.0 in an off grid PV
> system? Is it AC coupled only? Can it take generator power
> without barfing? What is the lead time on these?
>
> Many Thanks,
>
> Hilton
>
> --
> Hilton Dier III
> Missisquoi River Hydro
> Renewable Energy Design
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/f6ea4b30723a9bc5b29d047f6da2806b0296e922?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=b5c46602d9fb0d59>
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/8b291ee2dec6e8234cf52ede4191455626474080?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=ad1274bbc70810a0>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/836add2fd0522d76b8f2bbe2c2f6f9e28c187658?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=acb9de097dc846a7>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/ccc22d879d66d5c04a98a5c61d2625cc9d88ad5a?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=6e54e76130737629>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/c3567926e34d0ddc91e187d38e0390893398cf9a?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=b1afac8bc6ba3ed5>
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/ced87960a6603faabfa804649b2f1c5c4b5b3b47?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=5f935d7ea9bf964c>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/433222a0ac85c07cdc8ba1828518cde18ab5adf9?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=4c905b2fc1e823ba>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/76871e1902dfa610f585b1b8dc8d37803abea73b?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=0c1c1a6bc7f41415>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/27eaa17f79779836c455bbff32e18fd018424574?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=134646e4a1c18f11>
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/9887f4d348a66e425d01a57112af65ed37c6c499?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=c4b5dcfd78cf3e96>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/07092b59323827b81acf7a298b5f0a30c7d35ab9?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=1cc273a297a298b4>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/e2b1398da3d843e9f51f06dce9bf4f1b50c0ed2f?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=cbe1cd1484640e62>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/2bf40c8b8866f16c2ded3a68a6f703cd0b0c54c0?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=8b6b3c444e491b13>
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/ee5fe555334e1c91d60628c67cce819823f9657a?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=e20ae3b19e9fcdee>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/62a02cc889afa40d0ded59e2b4be33d0bf30d776?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=b60a2a8229423741>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/dc7807d233f3d021a21cfed7bd175235e3d866a0?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=1f083b0951b87587>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200721/c1d7d622/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Screen Shot 2020-07-20 at 2.32.24 PM.png
Type: image/png
Size: 50106 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200721/c1d7d622/attachment.png>
More information about the RE-Wrenches
mailing list