Yes but see Article100.1 for the definition of accessible and readily
accessible, to access you need a ladder. implies I think where the 8-foot
idea come from
I think this is poor writing, but it is accepted to be beyond reach
On Fri, Jul 17, 2020 at 11:02 AM AE Solar <autonomousenergies at gmail.com>
wrote:
> Kirk,
> Not sure if this helps but
> 690.31(A) “where PV source and output circuits operating at max system
> voltages greater than 30v are installed in readily accessible locations,
> circuit conductors shall be guarded or installed in a raceway”
>
> It doesn’t mention 8’ but mentions “readily accessible”. We have AHJs that
> interpret that as 8’ unless a 6’ fence is installed around the array. I
> don’t have a reference for those measurements though...just feedback we
> have gotten from inspectors
>
> On Fri, Jul 17, 2020 at 11:38 AM Kirk Herander <vtsolar at icloud.com> wrote:
>
>> All,
>> Is there a reference to this so-called "8-foot rule" that someone could
>> point me to in the NEC? Thanks.
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> --
> Adam Katzman
> Autonomous Energies
> PO Box 1245
> Kingston, NY 12402
> www.autonomousenergies.com
> (518) 567-1468
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200717/b518a99a/attachment.htm>
More information about the RE-Wrenches
mailing list