Kirk,
Not sure if this helps but
690.31(A) “where PV source and output circuits operating at max system
voltages greater than 30v are installed in readily accessible locations,
circuit conductors shall be guarded or installed in a raceway”
It doesn’t mention 8’ but mentions “readily accessible”. We have AHJs that
interpret that as 8’ unless a 6’ fence is installed around the array. I
don’t have a reference for those measurements though...just feedback we
have gotten from inspectors
On Fri, Jul 17, 2020 at 11:38 AM Kirk Herander <vtsolar at icloud.com> wrote:
> All,
> Is there a reference to this so-called "8-foot rule" that someone could
> point me to in the NEC? Thanks.