[RE-wrenches] Slave Radian not showing up on Hub10 or @ Mate3s

Roland - RES roland at renewablenergy.com
Thu Jun 25 15:05:32 EDT 2020


Hey Chris,

Sounds like a failed power supply board Outback part SPARE-215. If the unit is under warranty you should be able to get a replacement through OB tech support.  

> Sent from a IPhone, with touch screen keys on the fly. Please excuse shortcuts and typos. 
> 
Roland Shackelford
NABCEP CERTIFIED PV INSTALLER
President 
Renewable Energy Services (RES), Inc. 
Mobile:  808-938-9239
www.renewablenergy.com

> On Jun 25, 2020, at 7:35 AM, Chris Schaefer <chris at solarandwindfx.com> wrote:
> 
> 
> G'Day All,
> 
> So I started up a system recently with two Radian 8048A's. The master is connected to port 1 and the slave connected to port 2 with the FlexNet at port 3. There are no OB charge controllers in the system. When the hub is polling (led's scrolling) nothing shows up for the slave at port 2. It's like the slave inverter doesn't exist. So I moved the slave and flexnet down to port 3 and 4. No change in the polling. I swapped out comm (factory green) cables. Again no change. Looking at the control board of the slave there is only one green led on which is located at the upper right-hand side. Otherwise no led's are on. I have 57v at the buss bar terminals of the inverter. Of course since there is no polling at the hub there is no way to view port 2 to view the slave at the Mate.
> 
> Now the only thing that I didn't do was to try and use the manual on/off  switch-jumper to start the slave. But in the past regardless of the inverter being on or off it would still show up on the hub. This is  a new one and I'm looking for some direction here.
> 
> Thanks,
> Christopher- 
> Chris Schaefer’s
> 
> Tel/Fax 585-229-2083 or Cell 585-748-1870 
> 5115 South Hill Road ~ Canandaigua New York 14424
> www.solarandwindfx.com ~ E-mail: chris at solarandwindfx.com
> 
> 
> 
> Thomas Jefferson, the author of our great Constitution, once said, "democracy" will cease to exist when you take away from those who are willing to work and give to those who would not."
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20200625/c1824e10/attachment.htm>


More information about the RE-Wrenches mailing list